Setting up the Function file for the HSC as Mode 8 I think I only use the
A+ & B+ inputs on I:0/0/0 & I:0/0/1. Why do they show A/C & B/D for
the inputs on those (HSC:0) I am reading 1766-rm001 -en-p literature.
My encoder has A+,A-,B+,B- Do I only need the A+ & B+
I have used the ML1400 HSC before but never with an encoder that had +&-
My encoder is 2500 ppr if I use mode 8 with just A+ & B+ should I get 10000
ppr. I haven't done this enough to be familiar with it. Thanks
 