Hi everyone,
I am using a Micrologix 1400 and would like to communicate with a Eaton PowerXL DG1 VFD to pull the data registers for the speed, current and alarms. I am doing the speed control and start/stop via DO's and Analog outputs but would like to get more data to put on the HMI.
The manual says it has Ethernet/IP and Modbus TCP available. What is the easiest way to communicate with it over Ethernet? Modbus TCP or Ethernet/IP? I am thinking Modbus TCP but wanted to see if anyone has any other ideas.
Give me your thoughts.
Thanks!!
Modbus gets my vote.
Too many unknowns with EIP. Without looking at the manuals, I know ML1400 doesn't implement the full EIP standard. If Eaton only implemented (or only has experience using) the other half of the EIP protocol, you could potentially hit a brick wall.
Hi everyone,
Thanks!!
I do modbus TCP from the 1400 to Schneider Process drives all the time, it's really easy to set up. I have only tried EIP to a danfoss drive once, and had no end of trouble. In the end i think we could read most parameters we needed but couldn't control the drive.
I'd go modbus myself.
Hello, I am new here and have been working with PLCs for a few years now. I have been tasked with setting up a Micrologix 1400….. to a Cmore 10...
510
Hi, We may of finally received out first v21 ML1400. IP address set, proceed to download standard file for our machines & at about the 80% mark...
1,449
I have a Allen Bradely 1500 that has a cracked board. It still works but needs replaced (battery is no longer connected). To make migration easier...
3,231
Hi, I've got a new project for a vacuum conveying system. We require to add another HMI to the existing system which will then feed 2 separate...
1,838
Hi All I have connected a Keyence SR1000 to a Compact Logix PLC and am triggering the scanner and reading barcodes over Ethernet/IP, no issues...
848