mm420 question...
mitar
Oct 2004
zagreb
28
I'm controlling mm420 via plc s7-314 -2DP. When I testing my program everything is working fine. But than when I change the state of plc to Stop mode on mm420 start blinking F0070 and A0703. OK, I know mm lose data from PLC and it's OK. But when I try to change state of PLC to RUN mode again, nothing happens. F0070 and A0703 are blinking.
I can only move F0070 and A0703 with restarting mm.
Is any other way or I always must restart mm, when I change PLC to stop mode ?
You can cycle the power to the drive or
use reset-button in MM or
use digital input 3 (defaul setting) for reset the fault.
So, if you have some safety circuit, contol it by some PLC-output so when PLC not runs, it shut down safety circuit and MM lost its power.
When PLC is in RUN-mode, reset safety circuit after 5 to 10 seconds.
Or use some output for mm digital input 3.
There are not reset via Profibus, as some other manufacturers, or they not even need any reset !!??
http://www.siemens.com.br/upfiles/1529.pdf
Parameter P1210
Dear sir,
Can you try to change parameter P1210 to value 6. It will acknoledge every fail when it disappears.
Forgoselo
hi everybody, I am familiar with s7 200 PLCs snd i was wondering how can I write to PZD area or any other area ?? I mean I will use MOVE...
3,803
Hi Peepz, I would like to configure the drive as to control the speed via var resistor? AND another to run at two fix speeds, adjustable via a...
1,452
Hello, I am haveing problems getting a connection between my PC and a MM420 via profi adaptor. Never had these issues until may computer had to be...
2,220
I am new to the whole siemens programming. I have a s7-300 series PLC. ET-200S. I am typically installing GE PLC's. I finally figured out HW...
1,993
Hi everyone! I got a problem :bawling: when I do project on MM420 and CPU 313C-2DP. I read "MM4_Profibus Eng_lit8.pdf" and configured as the same...
1,638