I've got an M340 hitting an Ethernet to Serial converter one read at a time. Each read is enabled through a one-shot r_trig. I've got some extra time in between reads.

The CPU sometimes runs for awhile but eventually each read gets hung up with an error communication report 7. After that nothing gets the comms back except cycling power. I've tried the cancel bit, the cancel instruction, halting and back to run, shutting off the active bits before the read starts, etc.

Other posts on this forum seem to have found the same problem but I didn't see anything conclusive about a work-around. The CPU is in use in Alaska and they don't have a spare so updating the firmware concerns me. If I can tie it to a definite revision bug we can ship them a different CPU.

EcoStruxure V15

Thanks to all.
 
Sounds like data collisions on RS-side.


Have you used same gest parameters group for every read/write_var blocks?
As you can have only one modbus query active on RS232 or RS485 side, you don't need multiple gest parameters on M340 logic and sequencing and sending querys is easier to code.



This leads to that you need sequencer for communication. Add sequencer number every time with little delay when gest_parameter(1].0 is false.
(activity bit's false state enables ton timer delay for adding sequencer number)

Then you can communicate with this principle, only change you sequencer numbers to place of %S6 pulse before R_trig block.

http://www.plctalk.net/qanda/showthread.php?p=875957#post875957
 
Last edited:
One of the registers in the GEST management array is a parameter is a timeout. If this is set to zero then the failed communication will not time out, and everything freezes. Put a value in here.. it is in multiples of 100ms, so a value of 10 will give you a 1 second timeout

I forget which word it is but it is shown in the help file.
 

Similar Topics

Hey all, I am having an issue concerning the Modicon System Responsible for the operation of our Generator System. (Particularly Dresser-Rand...
Replies
5
Views
2,560
Hello, I'm having a hard time understanding how to get a Modicon M340 to pull a Modbus address from an ABB Totalflow via Ethernet. I set up a port...
Replies
5
Views
1,154
Hello. New to Unity and had a couple quick questions. Can a Modicon M340 output to a small multiline LCD screen and not a full HMI?
Replies
4
Views
967
Hi, I'm configuring the M340 controller with ATV320 inverters via Canopen. Everything was fine until today, when after starting the electrical...
Replies
1
Views
1,337
Hi, Does anyone know if programming a Modicon M580 is basically the same format as an M340? Also do they use the same software package? Thanks...
Replies
2
Views
1,779
Back
Top Bottom