I'm trying to retrive a project from a modicon PLC TSX P57104 with unitypro software, but when i connect it says ''No Upload Info''.

Currently the plc is in run mode and it also incorporate a MEM CARD.

Any suggestion how can i retrive the project?

Thank you
 
When you are connected there is an option under PLC to update upload info.
Do you have the option to transfer project from plc?
 
Modicon TSX

No there is no option for upload info, except backup option and when i do backup PLC to PC it gives error that the project is diferent and ask to write data on the PLC.

BR
 
The Upload Information storage can be switched off in the project settings, under plc embedded data, its normally switched off if the memory card is full to save space.

im assuming the last person who did the download did not store the upload information in the plc, you will not be able to upload the program, you will need the correct version of the unity file or you will need to download.
 
The Upload Information storage can be switched off in the project settings, under plc embedded data, its normally switched off if the memory card is full to save space.

im assuming the last person who did the download did not store the upload information in the plc, you will not be able to upload the program, you will need the correct version of the unity file or you will need to download.

Without upload information it impossible to upload program from Unity PLC, you need latest offline project for connecting online.
(original programmer maybe switched upload info off for reventing anyone else to connect plc without original program, or wanted to save program memory)
 

Similar Topics

Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
69
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
Replies
1
Views
156
Hello I was needing help with the proper scaling on a Modicon TSX Quantum- AVI030-00 8 Channel Analog Input PLC card. What would be the proper...
Replies
2
Views
1,498
Pure mind boggled at this one, can’t seem to figure it out. NO contact with - %M130(%MW11) How is this possible? Is the %MW11 0 it’s logic 0, 1...
Replies
5
Views
1,550
Hi All, i have PLC Modicon TSX 3722 Micro i need to know where should i put the socket of programming cable on Ter or Aux port. and i see the file...
Replies
0
Views
1,643
Back
Top Bottom