Module Has Blinking Green Light Indicating Its The Flow Meter

THEBOSS1011 said:
Question if I have a spare channel on that module cant I just hook the 2 wires to the spare or would it need to be configured

Yes you could do this..however..yes it wopuld need to be configured and the program would have to be changed to look for the values in the right place.. If you are not a PLC Guy then dont do this!! It could create major headaches if the values are referneced from more than one PLC..
 
Have you tried reversing the polarity at the I/O module? I've had AB analog cards that I thought were wired up correctly have open channel status. Reversing the leads sometimes is the answer.
 
I've had a single analog input fail as a result of a lightening strike. It's quite possible that whatever fried the meter initially.. also took out the input..
I'd recommend finding where that input is in the logic.. and switching the logic to using a spare input. Then hook the meter up to the new input. Typically (or .. hopefully).. they mov'd the input value to an integer and used the integer in the logic. That way you only have to change the single occurrence.
I did this months ago and it worked fine.


Good luck!
 
4-20 ma monitoring

Hi
Just connect the ( out ) lead of Flow to Ameter and the other lead of Ameter to input modul.
If current not read that means the wire broken.

regards

hanung
 

Similar Topics

I have a 4-20mA open circuit error on my plc. the flow meter was just repaired and reinstalled. The Amp had to be replaced on the flow meter due...
Replies
1
Views
4,833
I want to make some changes in Modbus configuration of communication module X COM 010 11 for HIMAX in SILWORX V11 but its asking me to cold...
Replies
0
Views
1,058
Last night I was trying to revive an old derelict machine after a slumber of many years. I couldn't connect to it with 1747-UIC cable from...
Replies
5
Views
2,136
Hi guys, I can only imagine how n00b this question is so please forgive me, but I've just started working with Allen Bradley Logix PLCs (5572 in...
Replies
9
Views
4,359
Has anyone ever calibrated an analog Input module for a PLC5? Was it worth the effort? I have a REV C 8 channel input module in a new project...
Replies
16
Views
6,990
Back
Top Bottom