We have a couple of S120 drives which are rack pinion system,which moves forward and back ward (linear motion only) . The drive shows Fault 7900 3 times per shift or sometimes more. The drive is commissioned for 6 -7 months. As per operator, it happens only during forward movements. What should I check. I checked the help file and it says to check below. I have increased the motor locked time but still the fault still comes up. Kindly advice

Screenshot_168.png Screenshot_167.png Screenshot_166.png Screenshot_169.png
 
You should set up a trace and monitor the current and torque

Has this occurred since day 1 of your startup?
 
Last edited:
I agree with JRW. You should also track encoder position and speed. I've had that fault before when the encoder wire had an issue; same thing where the machine was commissioned for months and it would happen randomly.
 
I agree with JRW. You should also track encoder position and speed. I've had that fault before when the encoder wire had an issue; same thing where the machine was commissioned for months and it would happen randomly.

Actually I am in remote support and I asked the customer to check the encoder wire for any damages. Was your cable damaged? or is better to change the wire to rule out any issue
 
Set your measure value acquisition to endless trace
download just the trace and start the trace with the arrow button

Watch the trace as it move back and forth

Can you do a screenshot of the expert list starting at about p300? and about the next 30 values down
That will tell us all the basic motor nameplate data
 
Last edited:
Your trace was there, but is now not visible.



My comment - you need to show speed demand as well as speed feedback - it would appear you have a synchronous motor so you can replace the current feedback with speed demand.
 

Similar Topics

I had trouble for a week trying to get a Marathon Symax Motor autotuned to work with a Powerflex 753 drive. I solved the problem and thought I...
Replies
0
Views
60
Hope you are doing well. Currently, I am involed in a revamping project. It requires to stop a mixer at specific postion. For the detail, this...
Replies
9
Views
313
I'm looking for how others do it. I need to start a 1 phase motor. I have always used a regular 3 phase Motor Protected Circuit Breaker and looped...
Replies
9
Views
251
I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
353
Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
178
Back
Top Bottom