Ok guys,
I've lost count of how many emg-gen I've hooked up to in the past. The most frequent problem is the frequency shift that takes place under starting current draw. Under normal power you may get low voltage, but the frequency holds, allowing the motor to get up to speed under no load. With emg power the starting load often boggs down the generator causing the frequency to drop, preventing the motor from getting up to speed, causing more current draw, causing the generator to bogg more ..etc.. until something tripps, or blows or whatever. Like I said, they are keeping me out of the loop, (no pun intended) as hard as I may try. I still hope aganst all reason that the generator may be sized properly, but it cant react to the sudden load for some reason. I'm not a standby power expert but I'm sure that can be fixed, as in the past.
It is not my responsability, or expertise to do a full energy audit of all loads connected to the generator. It is my contention that the generator should replicate normal power for all loads, including the elevator. The generator guy thinks differently, and has convienced the customer to do this. I am going to provide the owner with a document that will sheild me from liability in the event that the generator guy is wrong. He has agreed to it in princeaple, over the phone. However.. a new twist, he is going to ask the generator guy to assume responsabiliy for failure.
I'll bet that sometime tomarrow I'm going to get a call from the generator guy!
There will be a full blown document signing ceromoney before the project commences.
In the mean time I'm looking for a two ramp soft starter.
Allan, I found out the reason I have 5 of those AB starters. They trip out on very small frequency shifts. We had to replace them with contactors/heater overloads. I just cant win!banghead
I need something that will give me two ramps and 60hz. It looks like it may be a drive! $$$$ Theres a big edifference between drives and soft starters. A drive will have the capability to provide a constant or even ramping waveform dispite the incomming frequency. With the soft start it's GIGO.
APB,
EXACTLY!!! Thats my whole point. However if you read my posts I failed in my attempt to be witness to the "test". I'm not responsable for the entire building, I'm just the elevator guy.
Doug_P,
Good very good try, but that's not gonna happen, I'm sure your a very good programmer as your other posts indicate.
Rick,
I tried my best to explain the operation of the valve but I may have fell short. For more info (if your courious) check one of our suppliers HERE. http://www.eecovalves.com/
Eric,
You really do need to go back and explain to that guy about the concept of time, and how 24:59 dos'nt exist on our planet...not yet anyway. He'll have to wait a few million years for the rotation to slow a little.
Best regards to all, and thanks very much. This has been a great thread!
I'ts past 13 O'clock and I have to go to bed.
Mike.
I've lost count of how many emg-gen I've hooked up to in the past. The most frequent problem is the frequency shift that takes place under starting current draw. Under normal power you may get low voltage, but the frequency holds, allowing the motor to get up to speed under no load. With emg power the starting load often boggs down the generator causing the frequency to drop, preventing the motor from getting up to speed, causing more current draw, causing the generator to bogg more ..etc.. until something tripps, or blows or whatever. Like I said, they are keeping me out of the loop, (no pun intended) as hard as I may try. I still hope aganst all reason that the generator may be sized properly, but it cant react to the sudden load for some reason. I'm not a standby power expert but I'm sure that can be fixed, as in the past.
It is not my responsability, or expertise to do a full energy audit of all loads connected to the generator. It is my contention that the generator should replicate normal power for all loads, including the elevator. The generator guy thinks differently, and has convienced the customer to do this. I am going to provide the owner with a document that will sheild me from liability in the event that the generator guy is wrong. He has agreed to it in princeaple, over the phone. However.. a new twist, he is going to ask the generator guy to assume responsabiliy for failure.
I'll bet that sometime tomarrow I'm going to get a call from the generator guy!
There will be a full blown document signing ceromoney before the project commences.
In the mean time I'm looking for a two ramp soft starter.
Allan, I found out the reason I have 5 of those AB starters. They trip out on very small frequency shifts. We had to replace them with contactors/heater overloads. I just cant win!banghead
I need something that will give me two ramps and 60hz. It looks like it may be a drive! $$$$ Theres a big edifference between drives and soft starters. A drive will have the capability to provide a constant or even ramping waveform dispite the incomming frequency. With the soft start it's GIGO.
APB,
EXACTLY!!! Thats my whole point. However if you read my posts I failed in my attempt to be witness to the "test". I'm not responsable for the entire building, I'm just the elevator guy.
Doug_P,
Good very good try, but that's not gonna happen, I'm sure your a very good programmer as your other posts indicate.
Rick,
I tried my best to explain the operation of the valve but I may have fell short. For more info (if your courious) check one of our suppliers HERE. http://www.eecovalves.com/
Eric,
You really do need to go back and explain to that guy about the concept of time, and how 24:59 dos'nt exist on our planet...not yet anyway. He'll have to wait a few million years for the rotation to slow a little.
Best regards to all, and thanks very much. This has been a great thread!
I'ts past 13 O'clock and I have to go to bed.
Mike.