I dont profess to be a member of Mensa, however I do know the differance between soft starters, and solid state overloads.:rolleyes:

The remainder of your post is well taken.

Thanks, Mike
 
elevmike
I bypassed this one due to the subject - motor question for DickDV.

A very major part of my business in the implementation of diesel generator systems. I have seen this and many other problems before.

Basically, the generator should have been sized for the largest load step. kW ratings mean nothing if the first load step is large.

Generally speaking, a generator can accept a 40% load step as the first step. The second step is then open to negotiation. Some generators can accept a 100% load step. These are only supplied if specified as they are expensive.

The basis is that the generator manufacturer usually supplies the smallest engine he can for the alternator size. This means that load steps are usually small. I commissioned a job recently where transisents were to be tested at 25% load steps. The last section of load from 75% loaded upwards could only be stepped on in increments of 5% or the set actually stalled. Very small engine for the alternator size. First time I have seen an engine stall on such small load steps (25%).

It may not be the generator suppliers fault either. it depends on how the job was specified. If your motor draws a high current on starting and that size load step was not specified, it is not the generator rep's fault but the specifiers fault. HE SHOULD HAVE SPECIFIED THE LARGEST LOAD STEP FROM COLD AND ANYWHERE ELSE IN THE LOADING STAGES OF THE SET!!!!!

Generally, if larger load steps are required due to inrush of this nature, the engine is sized up to suit the application. Sometimes the alternator has to be sized up as well.

With the set manufacturer supplying the lowest sized engine he can (probably lose the job supplying a larger engine) the engine may be just sized high enough to drive the load but not to handle the load steps. Another manufacturer may not have an engine of that horse power rating and have to supply an engine with a higher horse power rating. this means that the set from that guy would handle bigger load steps due to a higher horse power. If nothing was specified he would probably lose the job.
beerchug
 
BobB,

Thanks very much for this enlightenment! I would have never thought of that, and it makes perfectly good sense!

Thanks for the new weapon!!! This may help me further my argument, and get the monkey on the right back.

(y)

Mike.
 

Similar Topics

We have an old liquid ring vacuum pump sitting in the parts area, and its been there for years. I got curious about it, was looking at it, and the...
Replies
3
Views
2,136
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,634
I don't run a UL panel shop or do UL designs, but I try to keep my designs UL friendly because several times I've had to have it inspected before...
Replies
4
Views
2,453
have a question. Hope i can ask it so it makes sense. Have a gear motor that is rated at 650 lb_in that turns 47 RPM at max speed. Need to use...
Replies
7
Views
2,122
I have a typical motor that can be wired for 230/460 but is also rated for 208VAC operation. It has a typical 1.15 service factor. If I wire...
Replies
20
Views
7,017
Back
Top Bottom