Could the O.P. please explain why Australian motors are easier to connect than American motors? I've never had the opportunity to wire one.
Thanx
Thanx
bulletin blues said:Could the O.P. please explain why Australian motors are easier to connect than American motors? I've never had the opportunity to wire one.
Thanx
bulletin blues said:Could the O.P. please explain why Australian motors are easier to connect than American motors? I've never had the opportunity to wire one.
Thanx
HJTRBO said:Hey all,
I'm very embarrassed to ask this question but I truely dont know the answer.
The machine was imported from the states 2nd hand (in great condition mind) and has a number of like motors that currently are all configured for high voltage.
The one i'll pick on is a 9 wire 7.5kW (10hp) motor that is internally star (wye) connected. The name plate voltage is 230/460V. It is to be hooked up to a Eurotherm 690 VSD.
Our system in Australia is 240/415V. Where the secondary of the utility supply transformer is star (wye) orientated. 415V phase to phase and 230V phase to nuetral.
I'm guessing that I will re-work the motors in the low voltage configuration. This will have a like pair of windings in parallel per phase with 240V dropped across them.
Is this the correct way to wire this motor?
Second side question, the motors are all wired in high voltage, so does that mean that there was 460V dropped across the 2 series windings. Go by root3 thats a line voltage of almost 800V???
Sorry to have to ask, but you yanks got me second guessing myself!
milldrone said:I must be missing something here. If I'm not mistaken your hz is 50 correct? I would think the motors will deliver the same torque at 415V 50 hz as when it's powered by 480V 60 hz. The only problem aside from some people being offended, is that the motors will be running at 5/6 the speed that they were in the states. Also the total horsepower will be 5/6 of what is was in the states. But the torque will be the same.