G'day,
I'm planning a fairly substantial upgrade to an existing plant system. It is a 10+ year-old installation and consists of 3x 1756-A10 racks connected over ControlNet. In order to not sit on an obsolete, unsupported time bomb, the goal is to replace the inter-rack comms with 1756-EN2TR units in a DLR configuration and upgrade the processor to a 1756-L72 (v28 firmware). Tentatively we're also replacing the system's 1756-ENBT with a 1756-EN2T dedicated to plant/HMI comms.
I've attached the before and after I/O trees.
That said ... the existing processor (v13 firmware) happens to communicate to an external ammonia supply system over its serial port by triggering MSG instructions. The MSGs' CIP paths are either of "2, 33" and "2, 34". As part of this upgrade, I'd like to plant a re-purposed 1756-L61 in the third rack and keep the original L55 beside it as a hot spare. These modules correspond to L61_DF1 and L55_DF1 in the new I/O tree, respectively.
I noticed I cannot set the L61/L55 serial port settings within the new project - do I need to build a separate Logix project for the L61 and possibly set up produced/consumed tags between it and the main L72, then trigger the serial comms within the L61 project?
Or do I simply place dummy projects on the L61/L55 with the serial configuration and trigger the main project's MSG instructions to use the paths "L61_DF1, 2, 33" and "L61_DF1, 2, 34" ?
Thank you for the help!
I'm planning a fairly substantial upgrade to an existing plant system. It is a 10+ year-old installation and consists of 3x 1756-A10 racks connected over ControlNet. In order to not sit on an obsolete, unsupported time bomb, the goal is to replace the inter-rack comms with 1756-EN2TR units in a DLR configuration and upgrade the processor to a 1756-L72 (v28 firmware). Tentatively we're also replacing the system's 1756-ENBT with a 1756-EN2T dedicated to plant/HMI comms.
I've attached the before and after I/O trees.
That said ... the existing processor (v13 firmware) happens to communicate to an external ammonia supply system over its serial port by triggering MSG instructions. The MSGs' CIP paths are either of "2, 33" and "2, 34". As part of this upgrade, I'd like to plant a re-purposed 1756-L61 in the third rack and keep the original L55 beside it as a hot spare. These modules correspond to L61_DF1 and L55_DF1 in the new I/O tree, respectively.
I noticed I cannot set the L61/L55 serial port settings within the new project - do I need to build a separate Logix project for the L61 and possibly set up produced/consumed tags between it and the main L72, then trigger the serial comms within the L61 project?
Or do I simply place dummy projects on the L61/L55 with the serial configuration and trigger the main project's MSG instructions to use the paths "L61_DF1, 2, 33" and "L61_DF1, 2, 34" ?
Thank you for the help!