Multilin 850 modbus in RSLogix

cstep7263

Member
Join Date
Dec 2019
Location
Katy, TX
Posts
35
Anyone know how to bring modbus data from GE Multilin 850 the correct way? None of the registers are lining up and data is coming in with values not looking correctly. There got to be an easier way.
 
Well if you are getting successful communications then you have it 2/3 whipped! Now you may be "off by 1" on the data addressing and/or need to word swap any registers that are long or floats (32 bits).

Here's an article that I skimmed that covers both of these common stumbling blocks.
Man, you've got that right! How you been, Okie? :)
 
Thank you for responding
Posting examples of what you sent vs what you received might help us to figure where it is getting tripped up at. BTW, this is a pretty common Modbus issue, But like OkiePC said, you've got 2/3rd's of it whipped.

And I always recommend using "middleware", at least during setup and troubleshooting, to remove any of the vagrancies of the receiving end. I downloaded this today: Rilheva Modbus Poll FREE Modbus RTU | Rilheva IIoT Platform I've no experience with it, but the price was right.
 

Similar Topics

Alright, here's the issue. We have a local rack connected via DIO to a second rack not far away. In that DIO rack we have a NOM card that is...
Replies
2
Views
2,009
Hello, I am having an issue communicating with a GE Multilin using a Redlion DSP. My goal is to get the RTD values from the multilin and write...
Replies
2
Views
3,113
Anyone put this together before? Im using gsd file gemu0c6d with 43 words in and 1 word out What settings have to be on the MM200? Ive read the...
Replies
0
Views
1,723
Hi guys, I have a Siemens CP341-RS422/485 module and I am trying to establish MODBUS communication to a series of Multilin269 / 469 protection...
Replies
1
Views
6,262
I have a 800hp 4160V induction motor (FLA 104) that is tripping on current overload and I have a question about the CT sizing. How can the motor...
Replies
5
Views
5,776
Back
Top Bottom