Hi all, I'm experimenting with using 2 1756-ENBT's in a single control logix backplane. My purpose is to eventually isolate some of my remote I/O on some of my systems to it's own network and off the overly populated plant network. ENBT_1 has an IP of 192.168.4.254. ENBT_2 has an IP of 10.0.0.1. In the IO tree I have added a powerflex 70 under ENBT_2 and assigned an IP of 10.0.0.2. I can communicate with processor via ENBT_1 and view and control both the ENBT_2 and the VFD. The issue I'm having is viewing anything using linx under ENBT_2. if I go to the drive properties page in the IO tree, select the far right tab, "Drive", I cannot connect to the drive. Linx appears and cannot find the drive because I assume it has a different IP than my laptop. I would like this to work so I can use automatic configuration feature. Any ideas?
 
What RSLinx driver are you using? To do this you'll have to use the regular Ethernet driver, not the Ethernet/IP driver.
 
I've tried using both drivers. I'm still having problems seeing the second Ethernet module with the different IP address. I can see it though the backplane, just not through linx. I may have to set up NAT on a managed switch. I've attached a screenshot showing the IO tree and the popup screen trying to connect to the drive.

Capture.jpg
 
Last edited:
Linx appears and cannot find the drive because I assume it has a different IP than my laptop.


I don't know for sure but think your on the right tracks here. In RSLinx you can setup your E/IP driver to browse a remote (as opposed to local) subnet. You could try adding a new driver for a remote subnet for your 10.. range
 
I don't have a live system in front of me and after I set it up, I don't do it for awhile, and I forget. o_O. But I as I remember, you need to right click below the ethernet card icon, where it shows a + and then you need to manually add the I.P. addresses of the devices that you want to browse to.
 
See technote:

26787 - Using Two Ethernet Bridge Modules to Create a Routed Ethernet Network
 
Your welcome. I use it when I need to configure a VFD that's on a separate EN2T (for I/O) from the comm EN2T.
 

Similar Topics

This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
146
Compactlogix controller, program has 28 conveyors that use TON's to start the conveyors. The TT sounds a warning horn during start and the DN...
Replies
10
Views
496
I have 9 field devices, three METSEPM5110 power meters and six ACE949-2 rs285 interface modules. I want to read this Modbus rtu data through rs485...
Replies
8
Views
317
I'm trying to use DTM browser to make make modbus poll from RTAC. I'm able to get the points in first poll object. But not able to get anything in...
Replies
1
Views
127
Hello, I encountered a problem with the kinetix 6500 drive, error code s22, loss of 3 phase voltage. After disassembling and replacing the thermal...
Replies
2
Views
170
Back
Top Bottom