Hi Guys,
Just getting back into programming after a long break !
Setup :
RSLogix 5000
FTView Studio ME
1769-L35E Processor
Pro-Soft MVI69PDPMV1 Profibus Module and a few other I/O cards etc.
Panelview Plus 1000 Compact
My question is this .......
The Pro-Soft card feeds I/O information into a controller tag that is made up as a SINT[1536].
There are two bytes of data within this tag
MVI69PDPMV1.Input[14] and
MVI69PDPMV1.Input[15] that are the speed that my motor is running at so I want to extract them and display them on my PVP.
Now I can point to each byte individually from the PVP but I need them combined as a 16 bit number to display the full speed value.
Ideally I also need this to work in the reverse direction so that I can enter a speed on my PVP and then write it to two other bytes which would set the motor speed.
I hope I have explained this okay, and hope that someone can help with this.
Many Thanks,
Mark
I would perform this function in the plc with a COPy command. It would look something like:
COP
Source: MVI69PDPMV1.Input[14]
Dest: ActualSpeed
Length: 1
where ActualSpeed is a controller level 16-bit integer.
To go the other way would be:
COP
Source: CommandedSpeed
Dest: MVI69PDPMV1.Output[14]
Length: 2
where CommandedSpeed is the speed setpoint as a controller level 16-bit integer.
The HMI would read ActualSpeed and write CommandedSpeed.
Keith
Thanks Keith that's excellent.
Just a couple of questions .....
Why length 1 then length 2 ?
The speed value can be a negative as it also sets the motor direction, does this confuse things ?
Mark.
The COP instruction copies however many bytes from the source element as are required to fill the destination element.
COP SINT INT 1 - Copies two bytes (SINT[0] & SINT[1]) to INT
COP SINT DINT 4 - Copies 4 bytes (SINT[0] - SINT[3]) to DINT
COP DINT SINT 1 - Copies the first byte of DINT to SINT
COP INT REAL 2 - Copies 4 bytes (two ints) from INT to REAL
COP INT SINT 2 - Copies both bytes from INT to SINT[0] and SINT[1]
COP INT SINT 1 - Copies only the first byte of INT to SINT[0]
As long as negatives are represented as two's complement, and the byte order is proper, this shouldn't be an issue, as it seems the input is just SINT type as a convenience, but actually can represent different values.
Close, but not quite. The length is always determined in the units of the destination type.
should be COP SINT DINT 1
should be COP INT REAL 1
I have problems with comm between MVI69-PDPMV1 and slave UCM22-FBP (V.4.00) (BB_082D.GSD)
in this moment led APP is ON and MSTR STAT is RED.
Please help me
my layout is: six slave (address 2,3,4,5,6 y 7) and block 60 word.
Back again with another question. I have an SLC500 modular rack with an open slot. I need to communicate with a device(EKM Metering electric...
18
3,752
I am working on a press that has a micrologix 1500 and a panel view 300. My problem is that sometimes some of the alarms are not being displayed...
1,962
Good Afternoon , I'm sure there are many Ishida Muti-Head Weigh Systems . We have a Ishida CCW-M-214W Multi-Head system . We are...
547
Hi all, have a project which requires reading a weigh head weight over ASCII. Never really touched ascii so struggling a bit. The weigh head is in...
1,247
Good Morning , We have a Ishida Multi-Head Scale . I had experiece with them for chips , crackers , etc. , but now we are using them for...
469