Networking 2 PLC's with different IP's
ceilingwalker
Mar 2010
Phoenix, AZ
1,586
Hello All, I have two CompactLogix that I would like to network together however, they have different IP subnets. Is there a way to connect them without using a router and without changing all the IP's from one to match the other? Hopefully this question makes sense. Thanks
We need more information.
What is the physical and logical configuration of the network path between them? Are they on the same Ethernet LAN (Ethernet broadcast domain, i.e. are they connected via switches, and see packets of each other's MAC address? Or perhaps even connected directly to each other?
What is the configuration of the current IP addresses, subnet masks, and gateway IP addresses for each? Can you change any of those values?
Do they have serial ports?
I'm assuming since you used the term subnet its just the last actual host ID your referring to.
Example PLC A is on 192.168.1.100 and PLC B is on 192.168.2.100.
If that is true, then as others have already said, adjust your subnet mask to allow traffic to flow. Instead of 255.255.255.0 make them 255.255.0.0
If they are wildly different, you could use a NATR as a router...
I know you say you don't want to use a router - but....it does sound like a job for the NATR if the IP are massively different.
Just saying.
Best practice in this example would be to set the mask to 255.255.254.0, but that is specific to a /23 network size.
For this example (...1.100 and ...2.100), wouldn't that need 255.255.252.0 to supernet the 0, 1, 2, and 3 networks? Asking because I am facing a very similar situation as the OP.
Sorry for the delayed response. A different "fire" required my attention. In my example, one PLC is 10.0.41.x and the other is 192.168.1.x. They both have other h-ware in their LAN's, which is why it isn't a simple matter of changing just one PLC's IP. As I type this, I have a feeling that a router is going to be the only way to make this happen.
yes, that sounds like the solution, especially if they are on separate LANs.
you could also put a second ethernet card (module) into one compactlogix and connect it to the other LAN, but a gateway between the networks is probably a quicker solution.
What CompactLogix? some have dual ports and it may be easier
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1769-um021_-en-p.pdf
Connecting to Different EtherNet/IP Network Topologies
The CompactLogix 5370 L3 controllers have embedded switch technology
and two EtherNet/IP ports that let you use it in different EtherNet/IP
network topologies:
• Device Level Ring network topology - Both ports on the controller are
connected to the network with requirements about how the
connections are made.
• Linear network topology - Both ports on the controller are connected to
the network with requirements about how the connections are made.
• Star network topology - One port on the controller is connected to
the network.
For more information, see EtherNet/IP Network Topologies on page 125.
Unless one of them is a 5380 with separately IP-addressable Ethernet ports, you will need a router, or a simpler NAT device such as the 1783-NATR or 9300-ENA, to perform the routing. The NAT will need to be at a location with physical access to both networks. For example, if located in the 192.168 panel, there will need to be a 10.0.41 drop into that same panel to plug into the public side of the NAT.
Hello All. I need to network two CompactLogix on different subnets. One is 192.168.1.22 and the other is 10.10.30.15. Since I have to bring a...
1,783
I have a question about IP addressing and Networking. I have a PLC with following IP address 10.1.0.120 this is an static PLC PLC is working like...
2,011
Hello all. I have a system with 4 different machines, each has their own PLC. I also have a RC in this subnet also. I created a server PLC that...
464
Hi Every one I want to hookup the 10 numbers S7 300 PLC CPU on MPI Network . CPU,s are running on 10 different machines with 12 " HMI on each on...
2,121
I have searched the forum, It looks like some people are doing a similar thing but I still have some questions. I have a number or PLC's, most...
4,740