In a Ring Network , we can configure device as Active Ring Supervisor and Backup Ring supervisors. In a single Ring network we can have only one Active Supervisor . But i would like to know what is the maximum number of possible backup Supervisor we can configure in a ring network.
Any help is Appreciated!!!
Thank in Advance
According to Rockwell and ODVA documentation, you have to configure at least one backup node (and they don't mention an explicit limit).
From Rockwell Automation Publication ENET-AT007B-EN-P:
While a backup supervisor is not required on a DLR network, we recommend
that you configure at least one backup ring supervisor for your ring network.
During normal operation, a backup supervisor operates as a ring participant. If
the active supervisor node operation is interrupted, the backup supervisor with
the next numerically highest precedence value becomes the active supervisor.
There is no requirement to have a Backup Supervisor. And there is not limit on how many supervisors are defined. Device with highest priority will become the Active supervisor.
If priorities are the same then MAC address will determine the active supervisor.
hi All Can you please help me to find the right software to open Zip backup of 434 12A PLC? Any major steps I need to know when opening? Regards
24
Is there a way to reset the count on the RS Logix BackUp?? XXXXX PROGRAM IN PROGRESS_BAK445.RSS XXXXX PROGRAM IN PROGRESS_BAK446.RSS XXXXX...
260
Please help me How to B&R 7CP476.60-1 upload program Backup and download which program should I use. Pvi transfer tool.? And how. Thank you
90
Hello all, I have an ABB PLC (PM573) and it has without MC card. I need to take backup from PLC to PC (in automation builder v2.7 ). My...
452
Hello everyone, In a factory where we installed Citect 7.20 the computer began to show the first signs of end of life. They never considered...
76