DickDV said:
...at heavy loads can get you into trouble since the drive cannot output more voltage than it gets in...
This brings up a question I have regarding motor nameplate voltage vs. incoming line voltage. Early this year, I had 2 A-D GS1 200V class 2HP drives fail within the first few days in the field from what I suspect was low incoming voltage. Both customers have 208V power, but I'll bet it only actually
REACHES that 208V on a 'good' day...
Both machines were used with 230V Baldor 2HP motors, so I had shipped them with the "Motor Nameplate Voltage" parameter set for 230V. According to Baldor, these motors are 'Usable at 208V', so when the customers replaced the drives, I had them set that parameter to 208V and have had no more problems since (Eric crosses fingers).
Since I was A.) Using these drives at their maximum 2HP rating, B.) Asking for 240V to the motor, and C.) Only giving them (at most) 208V, was I just asking for trouble? Also, does my changing the nameplate volts from 230 to 208V really help, or am I just pushing my luck?...
Since then, I have switched to the new Telmecanique Altivar 11 drives since my Schneider distributor beat A-D's (already low) price for the same size drive. These Tele 2HP drives have a M-U-C-H bigger heatsink than a 2HP GS1, so maybe they will better at withstanding any low voltage torture?...
In the future, might I be better off switching to a larger (say 3HP) drive? Or would that just be a waste of money?...
beerchug
-Eric
P.S. Here's a photo of the bridge rectifier in one of the dead drives. It doesn't smell too good either...