OI.MBTCP to COMX510

Jezz

Member
Join Date
Dec 2002
Location
Kendal
Posts
399
I'm trying to set up communications between a OI.MBTCP I/O server (for our historian) and a COMX510 that is on the same network , the COMX is also connected to some electric meters via Modbus Serial , now I need to get the data from the meters on to our historian.

So Question 1 is this possible ?

And Question 2 do I set up a Modbus bridge or ModbusPLC connection on OI.MBTCP?

Many thanks in advance
 
Although the COMX510 appears to be obsolete I see the User Guide and other documentation is still available at se.com.

I see "...data export with native connection to Schneider Electric service platforms
(such as Energy Operation) and with .csv file for other database servers"

FWIW
 
Finally got this working , I had missed enabling Modbus TCP on port 2 of the COMX 510 and to read that data I had to untick use concept data structures (reals) on the Node in the OI server , also had to enter the modbus address with an F after them to denote a 32 bit float:

E.G

402990 F
 

Similar Topics

Hi, We have an application that has a device that goes through a reboot (appears un-graceful) What then happens is the MVI module appears to hang...
Replies
0
Views
78
Hi. I'm struggling over some basic stuff here. 41001 I is a 16 bits integer that I'm able to read with InTouch. What I need to do is to read...
Replies
1
Views
96
Hi Friends, I have an upcoming project were I need 20 pcs of ModBus TCP Clients / AOI. to control 10 devices I use 20 transactions to control 10...
Replies
4
Views
747
Hi - I have a potential client who has a Wonderware / Aveva 2021 SCADA with the OI.MBTCP gateway installed. They want to get data out of their...
Replies
2
Views
829
I am configuring the Prosoft PLX32-EIP-MBTCP module for control Logix and DCS communication but the configurations are giving me an error. Anyone...
Replies
0
Views
1,023
Back
Top Bottom