Most I have come across is two loads switched on simultaneously using a single output point. Typically, an indicator lamp and a relay coil combination. Is there a downside to triggering 4-relay coils at the same time with using just a single output? Each relay draws around 42mA's (coil current). All 4 relays have free-wheeling diode protection built in. PLC output is rated for 2 AMPS per point. So when combined, all four relays draws fraction of what the output is capable of providing. Contacts from the relays are used as interlocks for other circuits and carry very low currents. (i.e. not switching on/off heavy loads) In order for the interlocks to function properly, all four relays must be in an on state. Failed relays (fused contacts, etc.), are accounted for via a separate monitoring circuit. Wanted to know the pros and cons of switching multiple loads using a single output. Any feedback would be greatly appreciated.