OK to Trigger 4 Relay coils with one output?

skyfox

Lifetime Supporting Member
Join Date
Nov 2006
Location
CA
Posts
279
Most I have come across is two loads switched on simultaneously using a single output point. Typically, an indicator lamp and a relay coil combination. Is there a downside to triggering 4-relay coils at the same time with using just a single output? Each relay draws around 42mA's (coil current). All 4 relays have free-wheeling diode protection built in. PLC output is rated for 2 AMPS per point. So when combined, all four relays draws fraction of what the output is capable of providing. Contacts from the relays are used as interlocks for other circuits and carry very low currents. (i.e. not switching on/off heavy loads) In order for the interlocks to function properly, all four relays must be in an on state. Failed relays (fused contacts, etc.), are accounted for via a separate monitoring circuit. Wanted to know the pros and cons of switching multiple loads using a single output. Any feedback would be greatly appreciated.


Cheers.
 
Last edited:
Most I have come across is two loads switched on simultaneously using a single output point. Typically, an indicator lamp and a relay coil combination. Is there a downside to triggering 4-relay coils at the same time with using just a single output? Each relay draws around 42mA's (coil current). All 4 relays have free-wheeling diode protection built in. PLC output is rated for 2 AMPS per point. So when combined, all four relays draws fraction of what the output is capable of providing. Contacts from the relays are used as interlocks for other circuits and carry very low currents. (i.e. not switching on/off heavy loads) In order for the interlocks to function properly, all four relays must be in an on state. Failed relays (fused contacts, etc.), are accounted for via a separate monitoring circuit. Wanted to know the pros and cons of switching multiple loads using a single output. Any feedback would be greatly appreciated.


Cheers.

I don't see a problem with it, so long as the total load is less than the output rating. I'd like to see separate fused circuits from the output for each of the relay coils.
 
Most I have come across is two loads switched on simultaneously using a single output point. Typically, an indicator lamp and a relay coil combination. Is there a downside to triggering 4-relay coils at the same time with using just a single output? Each relay draws around 42mA's (coil current). All 4 relays have free-wheeling diode protection built in. PLC output is rated for 2 AMPS per point. So when combined, all four relays draws fraction of what the output is capable of providing. Contacts from the relays are used as interlocks for other circuits and carry very low currents. (i.e. not switching on/off heavy loads) In order for the interlocks to function properly, all four relays must be in an on state. Failed relays (fused contacts, etc.), are accounted for via a separate monitoring circuit. Wanted to know the pros and cons of switching multiple loads using a single output. Any feedback would be greatly appreciated.


Cheers.


How about using one relay with enough poles to switch all the needed circuits?




-rpoet
 
Bit_Bucket & rpoet,

Thanks for the feedback. Unfortunately, I cannot use a single relay with multiple contacts. Circuit requires that polarity of the output and common be able to be reversed depending on the externally connected interface. For an example;

Device A1, A2, & A3 requires 24VDC to turn them on.

Device B1, B2, & B3 requires 0VDC to turn them on.

So I need to also switch the common leg from 0VDC to 24VDC when device type "B" is connected. This has to be done using the same PLC outputs which are at 24VDC. Hence the need for additional relays. A 4th PLC output is used to energize/de-energize interface relays to select between A & B devices as well as energize/de-energize interlock circuits depending on the device type being used.

Thanks again.

Cheers.
 
Unfortunately, I cannot use a single relay with multiple contacts. Circuit requires that polarity of the output and common be able to be reversed depending on the externally connected interface. For an example;

Device A1, A2, & A3 requires 24VDC to turn them on.

Device B1, B2, & B3 requires 0VDC to turn them on.

So I need to also switch the common leg from 0VDC to 24VDC when device type "B" is connected. This has to be done using the same PLC outputs which are at 24VDC. Hence the need for additional relays.
You have 2 potentials that you want to switch at the same time. 24V and 0V. Why cant that be done with a single relay or contactor with multiple (2) contacts ?
 
You have 2 potentials that you want to switch at the same time. 24V and 0V. Why cant that be done with a single relay or contactor with multiple (2) contacts ?


This.


All a relay does is connect (or disconnect) two points in the circuit for each set of contacts you use. It neither knows nor cares what you are connecting/disconnecting as long as you are not exceeding its contact ratings.


The only reason I can see you might want multiple relays is due to sheer number of things you are switching.
 
If it were me i would use an output for each relay the cost of the output in minimal then if later you find you need to split them it's just programming.
I see some are saying you use a larger relay with multiple contacts, keep in mind the larger the relay the more power it takes to pull in and hold in and the harder they are to replace if they fail.
 

Similar Topics

Hi i would like to ask! Im using Omron CP1E PLC May i know how to use one input to trigger two outputs alternatively? Meaning press X0 on, Y0...
Replies
11
Views
401
Hi all, I use e won for my OPCUA to back up my PLC (B&R X20 system) data. Whenever e won does maintenance updates, I need to reboot the e won in...
Replies
2
Views
480
Hello ladies and gents I’ve hit a road block on a project, it’s AB for preface this is a converting line including Winder tailsealer and...
Replies
4
Views
780
Hi, I'm using CX Programmer and just seeing what the best way to trigger an output from the plc clock time would be. I need this to come on at 9am...
Replies
4
Views
1,748
I am trying to have my Alarm Summary page open when an alarm goes active (I am using ALMD blocks) this is the expression I am trying to use...
Replies
5
Views
1,234
Back
Top Bottom