baba1511 Member B Join Date Apr 2005 Posts 19 Feb 12, 2007 #1 Hello all Please who can give me the n01 to n179 parameter setting for sysdrive 3G3MV Inverter to run in pulse train control. All contribution are welcome.
Hello all Please who can give me the n01 to n179 parameter setting for sysdrive 3G3MV Inverter to run in pulse train control. All contribution are welcome.
Leadfoot Member L Join Date May 2005 Location Red Stick, Cajun Land Posts 577 Feb 12, 2007 #2 You set N004 to parameter 5 to enable the pulse train control terminal. Terminal RP is the signal input referenced to FC the common. Parameter N149 is the scaling control for the pulse frequency.
You set N004 to parameter 5 to enable the pulse train control terminal. Terminal RP is the signal input referenced to FC the common. Parameter N149 is the scaling control for the pulse frequency.
baba1511 Member OP B Join Date Apr 2005 Posts 19 May 25, 2007 #3 Thanks I tried but it never work, I still need more help but I will check if there is open circuit. Regards
Thanks I tried but it never work, I still need more help but I will check if there is open circuit. Regards