Omron 3G3MV Inverter Parameter setting for pulse train

baba1511

Member
Join Date
Apr 2005
Posts
19
Hello all

Please who can give me the n01 to n179 parameter setting for sysdrive 3G3MV Inverter to run in pulse train control. All contribution are welcome.
 
You set N004 to parameter 5 to enable the pulse train control terminal. Terminal RP is the signal input referenced to FC the common.

Parameter N149 is the scaling control for the pulse frequency.
 
Thanks I tried but it never work, I still need more help but I will check if there is open circuit.

Regards
 