omron communication with PM500
amnart_j
Feb 2003
bangkok
I need connect OMRON PLC CJM1 with PM500 Power Meter modbus 485 module
The PLC consist of serial comm. RS232(1), RS485(1)
I assume you have an SCB card for serial communications. You will require CX-Protocol to write your modbus code and then communications are programmed in the PLC using the PMCR function.
CX-Protocol will allow you to write routines for any serial device.
beerchug
Hello everyone, I am trying to change the IP address of the Omron PLC (NJ30-1200) and HMI (NB7W-TW01B) to fetch the network on our network...
308
I'm hoping someone with experience here can help. I purchased a piece of equipment from a 3rd party vendor. This piece of equipment was...
2,680
I'm new to the Omron world and struggling a bit with transferring data from one NJ controller to another. The first thing I want to do is a...
1,013
I have a Omron CP1L PLC that I'm having problems communicating with a NS5-SQ11B-V2 Omron HMI through ethernet . I have the exact same set up on...
2,114
Hi; I have a DUPONT brand machine having OMRON PLC CQM1-CPU21-E. I have CX Programmer installed in my Laptop having W1indow10. I want to go...
3,634
