Omron CS1 serial port pinout.
Tharon
Jan 2007
Other
1,430
I've check the Omron website and looked through the CS Operation Manual, Reference Manual, and Programming Manuals. I'm looking for a pinout of the D-sub 9 pin RS232 Serial port on the CS1G-H PLC.
I have found some information from other vendors that show hook ups from their devices to the Omron CS PLC.
From that I have gathered that:
2 - TXD
3 - RXD
4 - RTS
5 - CTS
9 - GND
I am going to be sending a simple ASCII string out, so I believe I need to jump RTS and CTS together, but want to verify that pins 4 and 5 are the correct pins. Hopefully with some documentation from Omron.
The attached cable diagram should do the trick.
Pin 7 on the plc side is not required. That was for an older product.
Also, you will need to modify the setup of the port. Default would be HostLink.
You will need to change to RS232.
Hope this will help.
The logic seemed to convert nicely, and I had to make changes to the addresses for my AD and DA and 32-point input cards. The current problem is...
1,038
Guys, I am trying to configure a Variable speed drive on my ethernet/IP network on my CS1H PLC. All I need to do is read the speed, status etc...
1,573
Can I remove this unused module SCB41? I am Looking for reduce the power drawn from the power supply. I calculated that all modules in the rack...
1,611
I am an experienced programmer, but new to omron, but am working through that without too much trouble. I have a CS1W-PNT21 profinet card...
4,478
I'm looking to send ASCII strings through a SC1W-SCB21 communications module to a remote device. I've done similar applications with AB and with...
2,568