Omron PLC and ethernetmodule question
wwauters
Feb 2005
Brussels
I am working an a project with 8 Omron CS1G-CPU65 PLC's. Those are linked with controller-link. One PLC is equiped with an ethernetmodule and acts as gateway for the other PLC's. Each PLC has a cycletime of +- 70 ms.
The problem is now that if I want to read datawords from the PLC's from a SCADA on a PC, it takes a lot of time.
The communication between PC and PLC occurs via the Omron Fins Protocol. It uses UDP port 9600 to communicate with the PLC's.
What I found out is that a question from the PC is answerred after by the PLC 200 ms.
To check why it takes so long I've built a test setup with one PLC an a networkcard. After some test It looks like the delay between question and answer is caused by the cycle time.
So lets return to the project-setup (8 PLC's): If I want to question a PLC behind the gateway-PLC, I have to pass the gateway-PLC wich takes 70 ms, then ask the question to the PLC wich takes 70 ms, get the answer back wich takes 140 ms. This results in a total of 280 ms to receive ONE answer. Too long
Does someone knows a setting to use the ethernetmodule independend from the PLC cycle time (a kind of direct memory access)?
Any suggestion is welcome! Thanks a lot, WW
Hmmmmm, looks like my question ended up on page 5, after 4 days!!
Perhaps it would be a good idea to split the forums in several sub-topics....
Additional input: The PLC's are CS1G-CPU65 H, and the ethernetcards is a ETN21.
and UP ;-)
Have you tried using an OPC server? You can download a free demo from Kepware.
How fast are you looking to retrieve the data?
CS1G-CPU65 PLC's
You could replace the main CPU with a CS1H, they are much quicker, and more expensive of course.
Are you placing all your required information on the Controller Link network as global data before reading it out of the main PLC? Is Controller Link running at 2 megs? Any slower and their will be added overhead there also.
As you are using Controller Link, why not place a Controller Link PCI card in the PC? I find it works quite well. It would also alleviate the problem of a long scan on the nain processor because you would address each PLC individually. Usually find this a much better system than Ethernet, particularly reading all data out of 1 PLC. A lot cheaper also.
I have one Citect SCADA with a PCI Controller Link card in the computer where Citect kernel is reporting around 15,000 digital reads per second. A couple of hundred word reads as well.
The Controller Link PCI card is also a lot cheaper than a CS1 Ethernet module.
Hi There, I have couple of Omron PLCs connected on my kepserverex and my intouch reads data from kepserverex. I have been observing that roughly...
140
I am working on a project using a NB screen and NX1P2 PLC. I am having a really hard time getting a real number to properly translate through to...
121
Our plant manger/my boss wants each line to display the takt time above the line. I am trying to research the cheapest way to do this. Our plant...
191
I have PLC Omron CJ2M with OD211 module. I want to use the pulse output and PWM output and this module. But i confuse how to activated this, i...
113
I have a project to control the speed of motor DC using PWM Output on PLC and when im on working i have a several trouble and of of them is the...
220