I just tried firing up CapsJr. I only have one computer left with an actual parallel port, and it's not recognizing my dongle...
In any case, I made a quick ASCII version of the ladder in Notepad from 108 to the end. Any of the other Omron guys here want to check for typos?
| HDM
| 103 +---------+
|----]/[-----------------------------| START |
| | |
| 007 | |
|----] [-----------------------------| RESET |
| +---------+
| CNT0
| 105 +---------+
|----] [-----------------------------| COUNT |
| | | PRESET = 40
| 109 | |
|----] [-------------+---------------| RESET |
| | +---------+
| 012 CNT0 |
|----]/[-------]/[---+
| |
| 064 HDM2 |
|----] [-------] [---+
| |
| 007 CNT0 |
|----] [-------]/[---+
| |
| 003 |
|----] [-------------+
|
| 012 HDM3 003 076
|----]/[---+---] [---+---]/[------]/[------(075)
| | |
| 013 | |
|----]/[---+ |
| |
| 075 |
|----] [-------------+
|
| 071 075
|----] [-------]/[----+--------------------(076)
| |
| 076 HDM0 |
|----] [-------]/[----+
|
| 075 107
|----] [-------] [-------------------------(018)
|
| HDM2
|----] [-----------------------------------(014)
|
| HDM4 107
|----] [---+---] [-------------------------(019)
| |
| CNT0 |
|----] [---+
|
| 009 107
|----] [-------] [-------------------------(017)
|
| 011 107
|----] [-------] [-------------------------(016)
|
| 010 008 107
|----] [-------] [-------] [---------------(015)
|
|
|------------------------------------------(END)
FYI the 'HDM' is the high-speed counter. It increments each time the physical 'HDM IN' turns on (I'm guessing it's connected to an encoder?). Each contact (HDM1, HDM2, etc.) turns ON when its preset is 'in range' (like a drum sequencer). You'll have to view the current presets with the programming console. With the keyswitch in 'RUN', the key presses should be 'CLEAR', 'MONITOR', 'HDM', '0', and use the arrow keys to view each preset's 'FROM and 'TO' values.
000 through 011 are the physical inputs
012 through 019 are the physical outputs
105 is a 20ms clock pulse. It looks like the counter (CNT0) will expire after 8 seconds if not reset. Fault timer perhaps?
107 is a 1 second clock pulse. Might be used to flash a light?
109 is the first scan bit.
-Eric