one sensor two inputs
illibilli
Apr 2016
horsens
Just a quick newbie question.
Can I connect directly a digital sensor (reflective diffuse) to two independent PLC´s just by splitting up the cable, or is there a specific way to achive this. If it is possible on the other hand.
I'd the inputs are the same type you.could probably do it without the relay as well.
*Can* but probably *shouldn't*.
There was a thread about this exact topic a little while back - I'll see if I can find it - but the ultimate resolution was that yes, in very specific circumstances and if you take care of certain factors, you can make it work, but it's really not worth the potential headache when a $10 relay will do exactly what you want without any of the potential issues.
If a relay has 5 million cycles mechanical life specification, and activates every second, it's theoretical life span is under 2 month of continuous operation.
Also, relay may be not fast enough device for short signals.
I would connect the 0V of both systems, and split the sensor signal to both PLCs, directly or via isolating diodes.
Hello, i am a beginner with a Siemens Logo 8 PLC. I would determine the direction of an object if it passes a whole cycle of 2 input sensors. See...
196
I am a very inexperienced, self taught, plc programmer. I have taken Phil’s course, and have programmed a handful of Automation Direct DL05 plc’s...
2,336
The drawing shows the basics of what i am trying to achieve. The Hall sensor is drawn accurately from a schematic from the supplier. It is...
1,208
is there such thing as discrete logic gates for sensor inputs? I ran out of inputs for my plc rack I want to run a pair of sensor to a AND...
2,457
Hi, I've inherited an old machine that makes widgets. it runs well at 300Widgets per min, but any higher it gets flakey. This is a scan time...
31
10,155