OT: are 52a and 52b (Aux contacts) an ANSI standard?
I don't have a link to the standard, but when I did fossil/hydro work, anything "52" had to do with switchyard OCB's:
52CS - breaker control switch
52a - N.O. breaker aux
52b - N.C. breaker aux
thats the type of info I need.
I've found that 52Y is anti-dumping relay.
Anybody else work with these.
Somebody mentioned checking the IEEE red book?
Its for following prints on 13.8KV motor vacuum breakers.
thanks,
Brian.
If you do not need all of the specifics for each number, but rather want general descriptions, try a protective relay manufacturer like Beckwith.
Brian, the 52Y is actually referred to as the anti-PUMP relay. This circuit will prevent the breaker from reclosing if the close signal is held on and the breaker either trips free or receives the trip signal after the close. It is designed to prevent the breaker from cycling open-close-open-close (ie pumping) if the operator holds the close in the on position.
By the way, the standard is the ansi C37.2 and can also be found in the IEEE red book.
Bruce
1747-L542B vs 1747-L552B/C Besides the fact that SLC 5/05 uses Ethernet instead of DH+, are there any major differences between the 2 processors...
3,155
Hi all, I am searching operation manual on s5 module ip 252b. Could anybody please help me in this regard or give me some idea on this module...
1,475
Hi there, im almost going nuts! I've lost PLC program 'cause of dead battery and now im trying to upload it but can't find the cable. PLEASE...
3,012
Hi !!! I am a beginner. I try to connect to Hitachi H-252b (cpu22-02hb without EEPROM) in ActWin 3.28 all dip-switches on the cpu are set to off...
4,273
Hello all... I'm looking for a 480v 3ø 25+ amp Solid State Relay to replace a mechanical one beating itself to death keeping temp in a heating...
1,977