At 19 or 20 years old, you have virtually ZERO experience. Be glad you have a job.
I believe the Kid has bigger thing in mind. He will be running a company like this someday....
So, to summarize ideas from many users:
On each line there is a extrusion dies that has about 12-20 zones and a TC for each zone.
So you have up to 20 zones and thermocouples on each line. How many lines are there?
On the lines that have plc controlled zones, I limit the setpoint and I limit the output.
So not all lines have PLC controlled zones? How many do?
These dies have power and TC plugs on them because they are moved to other lines and changed out a lot.
From the jack back to the plc card is 50-70 feet on most lines. From the jack to the die it is 10-18 feet.
Hardwiring is not a option as TC stays with the die so it has to be unglugged and they move 2-3 times a week on average.
All zones control and go to the plc TC input cards.
So all thermocouples go to PLC input cards?
There are already policies in place to check things as they have been done. This is done by the line tech but most of the time done half a%&ed.
I was also thinking of running a loop for a dc digital input through the connector with the TC and use a different Pin on each and not allow heat contactor to engage unless the correct one is plugged in? What do you guys think?
Great idea.
We have grounded TC that get that way by being crushed from time to time and cause problems also. My TC input cards detect TC opens but not shorts i don't know what could be done to detect that.
But it does get old idiot proofing everything to the T and believe me i try. Some parts of the process you just can't idiot proof any further just the nature of the process and sometimes the management here that just goes right over their head.
Actually I have found that there is always at least one more way to idiot-proof just about anything. The key is to find the best, most practical method.
I like the RFID idea. RFID tags are cheap. Readers are a little on the expensive side. But if the pockets are deep enough and you ever wanted to play with cool new technology here is your chance.
I like it too, Alaric.
When it comes to idiot proofing, what I do is look at what the operator error is, and then what I can do to eliminate it. It sounds simple but a lot of times it isn’t.
Great technique, Clay.
Note: the color coding made the operators responsible for the hook up. Calling maintenance when you had tried to cross colors guaranteed the operator received disciplinary action. No way you could argue that if you had been paying any attention whatsoever you got the colors mixed up.
Coded, keyed, or colored connectors should do the job, but would require the approval of some higher up to fund the cost. I am not sure the Kid has such cooperation on this project.
Starting and testing the zones one at a time just won't work on this process. It would take too long. These are very large extruders and it takes a bit of time to see a good degree of temp change. It normally takes 5-6 hrs from cold for these boys to heat up and soak in and be stable so all zones have to be started at once.
Could the tests be done after a zone operation has started? If error found, alarm sounds, zone shut down, connections corrected?
Wireless would have to stay with the die and get torn up the first day here. I am going to have to stay with a plug-in solution. We do have a couple things on banner sure cross though they are really neat. Use the PLC if possible to help solve your problem. You can control the program and the costs.
Think on this for a second.
Time 0: start zone #1. Sense current.
Time 0 + 30: second look for temp Z 1
Time 0 + 60 second: measure temp z 1
All you are looking for is a temperature increase even if only one half degree.
Compare T 60 to T 30, AND if 60 more than 30, then turn on zone two, repeat for two. IF NOT, turn on check TC connection screen.
RFID - I'd go with readers in a base, beacons on the plug. When you plug it in get your plc to compare the plug. If wrong or missing then give an alarm or something.