It should, if everything goes according to plan, and the breakers are not full of metal shavings, accumulated dust and dirt, mouse dens, snakes, or insects. I know of one case (the old Diamond Shamrock plant in Sheffield, AL) where the second fault did not trip the 12kv breaker. The main tried to open (we assumed), but arced and started a meltdown. I was not there, thank God, but I saw it afterward. I could not recognize any of the electrical equipment. There was a pile of slag in the floor. The metal roof had burned off except for a few pieces around the walls. Pieces of hot metal had been blown in a circle all around the block building. The switchgear room, all breakers, busses, and the main 161/12 kv transformer were a complete loss.Actually, Lancie1, the second ground fault will open a phase breaker or fuse.
I think if the breaker had been able to open, the damage would have been limited. The switchgear was old and probably in need of cleaning. The ungrounded system did not cause the damage, but the fact that the delta-delta transformers allowed a first fault with no breaker trip lead to the second fault, which was not a mild easier-controlled phase-to-ground but a worst-case phase-to-phase fault.