output bits
this may be silly, but can you be more specific?
is the Output not turning on in the ladder logic, or is the field device not working?
point being- I am currently working on a PLC 5 120V output myself and at first I didn't realize they were isolated outputs. The card I'm using is a 1771-OD16.
From your description, the PLC output isn't turning on. If you have another ring of logic somewhere referencing the same output, the PLC will do whichever rung executes last.
Another thing to check - is the PLC in Run or Program mode?
If in a ladder other than Ladder 2, make sure there is a JSR to that ladder.
And do like Davek0974 says, right click on the output & click on Find All; in the results box see if there is more than one OTE, or maybe a OTU unlatch somewhere too. The last scanned line with the output rules.
I have two 1734-AENTR/B remote I/O racks attached to a 1769-L33ERM processor. Both racks are communicating; the inputs update in the PLC as...
3,106
Hi, I am new here and would like to ask for help on how I might go about re-using previously used CPU unit output bits in my ladder program...
49
8,229
Hello there, Sorry I am quite new to this... thank you for taking the time to answer my thread. I have a small problem trying to get an output...
23
5,123
My HMI (PanelView C400 TFT Color ) won't allow me to use an output address in a Tag. So I have to map the outputs to b3 bits. Is a Move the...
2,131
For example i have PLC with outputs with AO 8bit resolution. What does it meen, and what influence it gives?