Output/Input bits
I believe it means you have an Analog Output with 8 bits of resolution.
8 bits means that your full scale of output is either -128 to 127 (Or is it -127 to 128?) or 0 to 255. The more resolution it has, the finer tuned the analog signal can be. 10V/256 (8 bits) is less resolution than 10V/65536 (16 bits).
Edit:
Just to explain where those numbers came from. The bits are how many bits of binary are used for the output.
8 bits of binary is 2^8 = 256.
16 bits of binary is 2^16 = 65536
Edit:
so more bits meens biger precision of measurement and controling?
Yes.
But it also depends on the accuracy of the devices you are using for your input and output. A system is only as accurate as your least accurate device.
Don't confuse resolution with accuracy.
Accuracy is the difference between the "right" value and the actual value. A lot of things influence this, and I've seen 12 bit and 16 bit I/O that had a lot of drift and error.
Resolution is the number of decimal places or digits in the display. It isn't the same as accuracy. You can display a wrong answer to 20 decimal places.
And look at the resolution required. 1/256 = 0.4% If you have a 1% accurate sensor or a valve positioner that is ±2% (which some are) then additional resolution probably won't give more accurate results.
How can I use 1 button and 1 light using only b3
267
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
361
Hi i would like to ask! Im using Omron CP1E PLC May i know how to use one input to trigger two outputs alternatively? Meaning press X0 on, Y0...
403
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
18
1,446
Hello! I have a FB with inputs, outputs and inputs-outputs. The build finishes with error, if one of input-output isn't connected. I need an extra...
448