Output checking
jandrul
Jan 2013
NY
How does output checking work ? NFPA87 calls for output checking in chapter 8. What is output checking ? Thanks
Basically it means using some sort of feedback that the action the output was to perform, actually did. So, if you tell a valve to shut, then you need some form of indication that it did indeed shut (limit switch on valve, pressure switch downstream, flow sensor, etc...). Since the NFPA87 is concerned with fluid heaters, safety of the fuel source is a concern. When you tell a fuel valve to shut you want to ensure it did to prevent unexpected fuel leakage and possible explosion or fire. Output checking in this case would cause a alarm or further shutdown measures to occur if an output device fails to operate as instructed.
Thanks for your reply Mark, that makes a lot of sense. I am involved with upgrading an obsolete PLC on a thermal oil heater. One of our objectives is to ensure that the new PLC will comply with the new NFPA code. In order to comply with the output checking stipulation we may need to add some instrumentation which will likely increase our scope. Thanks for your help Mark
Hi, I am validation engineer. currently i am working on S7 300. i want to know how to check the analog input and output ? can i take a screen...
1,754
Hi, how do I find out if my input or output work or not. I have a switch probe and a indicator light. I'm using omron zen v3 to program. I check...
2,566
Hi There, I have a filler with a coriolis flowmeter that has died. the filler requires a pulsed output (manufacturer wont edit the program) is...
265
Hey all, I am starting a new project for a customer and I am adding in solenoid valves. Once added, I noticed there was a lack of an Output...
90
Hi, The hardware is: Click Plc model # CO-O1DD1-O HMI model # S3ML-R magnetic-inductive flow meter model # FMM100-1001. I will set the flow meter...
193