PACTare Comm Issues WIN 7

tpal79

Member
Join Date
Feb 2013
Location
Houston,Tx
Posts
6
Having an issue with PACTware 4.1 running on WIN 7. I keep getting a communication error when trying to get the online parameterization of a DTM for a Turck temperature module. No problem with the software on a machine with WIN XP. Any help is greatly appreciated.
 
PACTware Comm Isues

No cannot talk to any other devices, but I'm using a HART comm multiplexer and it connects no problem.
 
There are continuing revisions of HART. HART 5, HART 6, HART 7.

Pactware has a HART driver. It gets revised on occasion.

I know I had to find a revised HART driver to be able to talk to a recently released HART 7 transmitter. The vendor supplied a link to the revised HART driver that could talk to their HART 7 transmitter. They supplied the DTM as well, but the DTM talks 'through' the HART driver.

I suspect that your HART driver is not a recent enough revision.
 
PACTware Comm Isues

Are you using WIN XP or 7. If you are using 7 could I have the site where you where able to find the Hart driver?
 
I run Pactwware in Win 7 but I suspect it is a HART version issue as much as a Windows thing.

In Pactware, the HART DTM version number is displayed - the graphic shows the DTM version 1.0.44 after I updated.

dftjq.jpg


HART Communication DTM : a free version of HART Communication DTM is available for download from CodeWrights website.

HART Communication DTM download:
Go to http://www.codewrights.biz/

There's a download link to the HART DTM from the right side window on the home page:
2nlvfhl.jpg
 
PACTware Comm Issues

Well I checked the HART DTM and I was using the same one 1.0.44.So I am thinking it is the TURK DTM that is the culprit.
 
1) Do you have 250 ohms resistance in the loop? No HART without 250 ohms resistance.

2) You're probably using a USB HART modem?

Have you checked which COM port it installs on (each USB port on a PC is a different COM port) in Device Manager and set the HART com up for that port?

2wf44xu.jpg


zu4ir.jpg
 

Similar Topics

Hey guys. As the title suggests, I need to configure a Danfoss Aquadrive FC202 inverter, so that its logic inhibits the local command when the...
Replies
2
Views
52
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
Replies
16
Views
525
After updating a panel, I inherited another PLC for my "learning lab". It's a Modicon TSX Micro. I've not worked with a Modicon PLC yet, so I...
Replies
1
Views
141
Guys need a bit of help getting the instance correct for a 22comme with a PF40P. Trying to get 2 things first is the drive current amp draw...
Replies
1
Views
96
I have 3 new PowerFlex 7000 VFD's. Rockwell was out to do some checking before startup. These are part of a larger electrical project. I gave the...
Replies
7
Views
333
Back
Top Bottom