panel builder 32 help
sweetjohnny
Feb 2012
Iowa
55
I am not well versed in PB32, so i am needing some direction I will be short and direct.
I have a panelview 600, communicating to a slc 5/04.
In my system I have a Sensor that reads a mark, when this sensor is flagged x amount of times it triggers an output. The sensor input is tied to a CTU instruction with a preset value.
My question is, can I write directly from the PV to the CTU instruction to change the preset value? Also, how do I create tags and whatnot in Panelbuilder 32?
Yes, if you want to change how many counts that the CTU will count to before turning on its DN bit, then write to and change the PRE value.
In PanelBuilder, create a new Integer tag, and link it to your CTU Preset PLC address. See "Defining Tags", Chapter 19,Page 19-5 in the PanelBuilder Software User Manual.
It is best to write to an integer word first then move that value to the counter's preset. That way you can test the value for limits before writing the counter's preset.
Mickey,
Luckily with PB32 you don't need to us a LIM. When defining tags, one of the parameters available is "Data Entry Limits".
Here you can set the min and max values that can be assigned to the tag.
It will even display the range in the numeric entry object. Nice feature! ;)
G.
Mickey,
G.
I still like to do it in the PLC.
Hi guys I have a question to see if it is possible to display a cycle timer slide display on a panel view screen ? I have a machine that we...
1,970
Ok I am using panel builder 32 and a allen bradley panel view 550. So I put a got to screen slector and I can go to objective properties and set...
3,150
Does anyone know where I could download panel builder 32 for old rockwell HMI's? Our supplier is no help and we are struggling to find the...
901
When using Panel Builder 32 I am adding a tag and the array size seems to default to 0 on floats and integers. I am wondering if this will...
1,132
I just finished making my 3rd service call to a large machine shop, troubleshooting PLC issues. I can see that none of the PLC or HMI programs are...
3,054