Sorry for the late reply...
As I'm sure you know, within the application you need to change the PanelView Plus terminal type from 1250 (not 1200) to 600 under the
Project Settings. The 1250 uses a resolution of 800x600 pixels, whereas the 600 uses a resolution of 320x240 pixels.
The scaling of the displays, objects and text is the biggest concern with such a change in resolution. The general practice is to select
Scale graphic displays to rescale everything.
Once you select this option you can then further decide whether to scale the font size used by the objects on the displays, the border sizes, and also any image files stored in the image folder.
The rescaling of images can be tricky and its success depends a lot on the original image's size and complexity. It doesn't always work out so well.
Here is some info on the conversion...
60659 - FactoryTalk View ME : How can I resize the displays to fit a new resolution
Access Level: Everyone
60661 - FactoryTalk View ME: Changing the scale of a display
Access Level: TechConnect (Also linked in the above technote)
Take stock of the advice to backup the original application file before attempting to resize/rescale. The scaling will usually not revert back properly to the original size if you decide to back track.
Regards,
George