Hi
I am trying to communicate panel view plus compact([FONT="]cat no. 2711PC-T6C20D[/FONT]) to MicroLogix 1200 through Serial RS232(DF1 protocol). But i cannot find my HMI in the RSLink. but i am getting my plc in the rslink.
The Physical connection from my pc to PLC and HMI is in Ethernt And in RSLink i am looking under EtherNet/IP driver. I am getting my device in the RSLink. but when i am going to Tag Browser in factory talk then the online tags are not showing.
confirm that your E/net addresses are correct.
both the PLC and the screen need independant E/net values
But the Screen needs to know what the PLC address is and the PLC type
have you set that?
confirm that your E/net addresses are correct.
both the PLC and the screen need independant E/net values
But the Screen needs to know what the PLC address is and the PLC type
have you set that?
Hi
I am trying to communicate panel view plus compact([FONT="]cat no. 2711PC-T6C20D[/FONT]) to MicroLogix 1200 through Serial RS232(DF1 protocol). But i cannot find my HMI in the RSLink. but i am getting my plc in the rslink.
I really don't think this system could be functional.
PanelView Plus Compact terminals were developped for Logix (Flex-, Compact-, Control-)systems integration.
MicroLogix 1200 is not a Logix system.
The PanelView Plus applications data server, RSLinx Enterprise, is not deployable on a Logix 5/500 system unless a communications module buffer is implemented.
The PanelView Plus Compact family does not offer any communications modules options (only the PanelView Plus family does so).