Panel View w/ Devicenet
JeffB
Apr 2002
NW Arkansas
79
Hello,
My current project calls for using an A/B Panel View configured for Devicenet communication and a SLC 5/04. This is the first time I've used a Panel View configured for Devicenet. Am I limited to 32 words of I/O? Is it possible for me to access the SLC data table directly from the P.V.?
Also, I'm considering using the COS "change of state" protocol to communicate with the SLC. Would this be appropiate for an application that uses a PV to emulate push buttons and selector swithes?
Thanks for any and all replys,
Jeff
Get ready for a surprise; the DeviceNet PanelView is a lot more like the Remote I/O units than it is like the DH-485 or DH+ ones.
You can't directly access the controller's data table; the B:xx and N:xx addresses you're familiar with in the SLC won't be accessible.
Instead, the PanelView exchanges a block of I/O data with the 1747-SDN, that you configure in RSNetworx for DeviceNet. I almost always use Change-of-State for this connection, because it saves on bandwidth and that's important, because it's usually a fairly big connection.
The DNet PanelViews make up for their less elegant exchange of data with the scanner module by having terrific abilities to interact with other devices on the network. You can set up "listen only" connections to consume data going from slave devices to the controller, as well as explicit message tags to extract data from devices like drives and overload relays directly.
I wish the PanelView firmware designers had given it the ability to use the explicit message services "Get Member" and "Set Member" so it could randomly access parts of the 1747-SDN discrete and M0/M1 data files. As it is, if you define an explicit message to the scanner you have to read the whole darn data table.
The 1747-SDN can also send explicit messages to the PanelView's Explicit Server connection memory, similar to the way that a Remote I/O PanelView gets Block Transfers from a PLC-5 or SLC. Those messages are a little difficult to format the first time you try; get an example or some help sending Explicit Message instructions.
I have a PV 1000 T10C10 Ser B That has from the factory the DeviceNet communication card installed. I am wondering if it is possible to change the...
2,891
This is one of the assembly stations, which are very typical in our plant. Panel View PV-600 is one of the nodes on the DeviceNet network (SLC...
13,871
I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
208
Am asking if we can upgrade sd ram and cf card of panel view plus ab by a normal sd ram and cf card but Allen Bradley to save cost because in ab...
283
I can't seem to get the Panel View Plus 7 standard edition to downgrade to V_11, when I check the AB downloads and compatibility websites for this...
141