Using the kfd2 series in a panel, do I need to put +24v on terminals 14 and 15 as well as on terminal 7 to the transmitter?
thanks yall
The isolated barrier does require 24V to power up the barrier itself. This can either be on terminals 14/15, or you can use this Pepperl Fuchs power rail. Terminal 7's connection will change depending on how you want to use it. Check out the output section of the datasheet on page 2. There is also a diagram for this on the bottom of the datasheet.
Hi experts, I hope you're all having incredible days. I'd really like to utilize this sensor for a customer application, but the issue is that...