Pepperl-Fuchs Isolator power supply

wire_god

Member
Join Date
Sep 2019
Location
Newfoundland
Posts
3
Hi guys

Using the kfd2 series in a panel, do I need to put +24v on terminals 14 and 15 as well as on terminal 7 to the transmitter?

thanks yall
 
The isolated barrier does require 24V to power up the barrier itself. This can either be on terminals 14/15, or you can use this Pepperl Fuchs power rail. Terminal 7's connection will change depending on how you want to use it. Check out the output section of the datasheet on page 2. There is also a diagram for this on the bottom of the datasheet.
 