PID tuning
initially how to tune a PID for temp control. is there any relation among P, I & D while tuning.
Regards
Manasi
Short answer yes. Each can affect the other.
I suggest you do a search on P.I.D. tutorials. There are several. Look for those with the easy math. You'll see what I mean when you look into it.
I would do a search at this forum first, if that doesn't pan out, try Google.
You do not always need P.I.D. depends on the system, and amount of control and response needed. Most tines you need the P and I, on a dynamic system you will most likely need all 3.
Regards
Manasi
Hello manasi;
Since you seem to be in your first steps in PID tuning, I would recommend that you search on the posts presented in this forum (and on his own site) by a gentleman named Ron Beaufort.(Look for the SEARCH link at the top of the page). He especially has 3 linked articles that you should look at: What is "P" in PID, and same for "I" and "D". They offer a very good, clear and low-math initiation into the principles and application of the PID control principles; they also explain the interactions of the different parameters on the control output, and on each other.
You would be much better prepared to implement PID in your project and future ones.
Hope this helps,
Daniel Chartier
Edit: here is a link to "P in PID", it containk the required links to "I in PID" and "D in PID". Good reading!
http://www.plctalk.net/qanda/showthread.php?t=13459
Manasi,
While I am by no means an expert with PID control I have found that temperature is one of the easiest processes to control. That is, compared to others I have had to do such as chlorine, pH, and ozone. I pretty much never use Derivative and normally use a small amount of Integral with the Proportional being my main adjustment.
Yes, auto tuning programs have worked out the math that calculates the gains after analyzing there the response of the system to excitation.
Every system is different so what works for one system may not work for another system. I would go to www.controlguru.com and read the part about tuning a heat exchanger.
Actually flow loops are the easiest to tune because the response to a change is almost instantaneous whereas temperature can have lots of lag. As rta53 says D is the most difficult term to utilize successfully.
I suggest you forget the math and do a search for Ziegler and Nichols, their tuning method is quite easy to understand.
Roy
That is because:
1. some systems don't require derivative gain mathematically. Do you know which ones?
2. The feed back resolution plays a big part. Most of the noise people complain about is really due to quantizing.
3. Sample jitter. PLCs do not have a constant scan time and even the interrupts have a lot of jitter. Sample jitter results in poor rate estimations.
Roy
ZN results in poor response that over shoots and the oscillates around the set point a few times. One can do much better with just a little effort. The methods on the www.controlguru.com are much better than ZN.
Once you understand the math you will never see PID tuning the same.
PID is the best technique bUt however P,PI.PD can be used in some processes with great results.these parameters rely on each other especially in critical loops
Hi, Manshi,
I have some experience with temp. loops, try the following, hope you will get good result. but before that I need to understand what is your temp. source, ( thermic fluid, heat exchanger, electric heat generator Star/delta) etc.
keep, i & d =0.
put p (kp) to a little high, try to check three cycle, if required put some I, to adjust. you might not need D, use dead band to stabilize ( if your process permit.
Thanks Bhaskar
I would make one guess: In flow controll you should not use derivative term?
You are right. The general rule of thumb is that one gain is required for every pole in a system. Do you know what a pole is?
PID isn't always the best technique. It really does depend on the application. Ki is usually required on type 1 systems where reaching the set point exactly isn't required. Kd isn't required in most speed control applications. There is a mathematical justification for these statements.
keep, i & d =0.
Superstition without mathematical justification. A temperature control system has dead time because it takes time for heat to move. It has one time constant which is heating the thermal mass or the load. There may be another time constant and that is the time it takes the temperature sensor to respond to the temperature of the mass being heated. A type 0, temperature or velocity control system, requires a integrator. If there is a time constant due to the thermal mass. This requires a P gain. If there is also a time constant due to the temperature then a another gain is required, the derivative gain.
No i do not know what a pole is (google does not give anything i recognice to explain what pole is). But i believe you'll explain it to me.
That flow controll thing i knew only becouse my teacher some six years ago once told us that we should not use D-term in flow controll. Altough i cant remember why that was. At only 23 years i have lot to learn;)
Thanks in advance.
I agree on ziegler nichols tuning methods, the initial parameters that are calculated via the Z-N tables are really just a starting point but will most probably require some fine tuning.
Just a comment on Derivative and Flow control, i believe the reason for not using derivative is that with flow you may get some spikes and fluctuation in the signal and due to derivative term operating on the "rate of change" of the error this would generate derivative "jerk".
Hello, I am attempting to tune a PID loop on a process. The process involves a valve with electronic actuator that has quite a high deadband...
2,206
so i have 4 25gpm wells feeding a 1000gal tank (T-1), with an additional 15gpm from a decant tank for 3hrs every 12hrs. P1 and P2 both controlled...
154
35,950
Hi everyone, yet another PID problem. I'm hoping I understand enough of the process I'm controlling that my request for help is reasonable. If a...
113
28,323
A few months ago, I started to look into PID controllers and the tuning of first order processes. This has, partly thanks to you, resulted in a...
162
62,797
I haven't had to tune a PID loop in a very long time. It's actually a PI loop for a pulse width modulation s.v. What was the name of that tuning...
16
4,141