Hello, I have a problem with Factory TalkView Studio.
I have been programming loops RSlogix 5000.
I have a tag called DrumSP (Real) going into SPOper of the PIDE and when I write into it directly within rslogix 5000 the output SP of the PIDE it holds the value. so if I write a 5 in SPOper I get 5 in the SP and it holds forever.
if I go through the FactoryTalk view Studio and I have used the numeric input enable connecting it to the tag DrumpSP and when I put the value lets say 5 It goes to 1 and then 0. if I put 60 I get 0 it just goes back to zero. why does it resets?
*important*
When in PIDE is in auto is for example CV=40 (Auto) and I go to manual
CVOper input. as long as I keep inputting CVOper values between 1-40 it will hold its value on the CV output. If I happen to put a zero in CVOper any number that I put later will be reset to a zero
All the zeroing issues above are related only to when inputting values from FactoryTalk View Studio.
if I use RSLogix 5000 it has never given me a problem. PIDE is on ProgOperReq=1 and taking operator inputs at this point.
to summarize
through RsLogix
tag= DrumSP(REAL)-> 5->SP=5 doesn't reset to zero
through FactoryTalk view Studio
numeric input enabled ->tag= DrumSP(REAL)--> 5 -->SP=5 it does reset to 0
I have been programming loops RSlogix 5000.
I have a tag called DrumSP (Real) going into SPOper of the PIDE and when I write into it directly within rslogix 5000 the output SP of the PIDE it holds the value. so if I write a 5 in SPOper I get 5 in the SP and it holds forever.
if I go through the FactoryTalk view Studio and I have used the numeric input enable connecting it to the tag DrumpSP and when I put the value lets say 5 It goes to 1 and then 0. if I put 60 I get 0 it just goes back to zero. why does it resets?
*important*
When in PIDE is in auto is for example CV=40 (Auto) and I go to manual
CVOper input. as long as I keep inputting CVOper values between 1-40 it will hold its value on the CV output. If I happen to put a zero in CVOper any number that I put later will be reset to a zero
All the zeroing issues above are related only to when inputting values from FactoryTalk View Studio.
if I use RSLogix 5000 it has never given me a problem. PIDE is on ProgOperReq=1 and taking operator inputs at this point.
to summarize
through RsLogix
tag= DrumSP(REAL)-> 5->SP=5 doesn't reset to zero
through FactoryTalk view Studio
numeric input enabled ->tag= DrumSP(REAL)--> 5 -->SP=5 it does reset to 0