I spent a couple of hours flying through turbulence over the Rockies and familiarizing myself with the old Prosoft User Manual. Once you are familiar with it, it's really pretty straightforward.
From what I can tell, the logic has some configuration mistakes that won't cause malfunctions but make the module run inefficiently.
For example, Rung 01 causes three BTW's of 50 words each to move 150 words of PLC-5 data from N16:0-149 to the Prosoft module's database words 0-149. All these words are zeroes and the Prosoft module doesn't send that data to any of the connected devices. It's a waste of memory and time but it doesn't hurt anything.
Also, the configuration sent to the Prosoft card in Rung 01 uses two blocks of 5 Commands each to actually transport 4 Commands, of which two are duplicate commands. Both Node 14 and Node 16 appear twice in the Poll List. Again, it doesn't hurt anything but it wastes time and memory.
Probably the best way to explain this is to show the contents of the PLC-5's N15 data table with the associated Prosoft block numbers and function labels, as well as an end-to-end illustration of what data in the SLC gets read into the PLC-5.
The existing logic reads N9:1-15 from the SLC at Node 16 on Channel 1 and places it in the PLC-5 in N16:200-214.
It also attempts to read N9:1-9 from the SLC at Node 14 on Channel 2 and place it in the PLC-5 in N16:150-158, but either this data is not being successfully read from the device on that channel or the data is always zero. This may explain the presence of the ERR LED on this Communication Module.
Your stated goal was: "Now I need to transfer (N7:50 - N7:62) from SLC 5/03 of WTP to this PLC 5/20, and connect to RSView using tags at N7:250 -N7:262 "
Add one new Command to the Command List:
Code:
N15:170 1 Block 82 Command 3 Port ID
N15:171 16 Block 82 Command 3 Slave Node Number
N15:172 11 Block 82 Command 3 Function Code 11 = SLC500 Word Range Read
N15:173 220 Block 82 Command 3 Module Database Address
N15:174 13 Block 82 Command 3 Word Count
N15:175 7 Block 82 Command 3 Data File Number
N15:176 137 Block 82 Command 3 Data File Type (137 = 0x89 = Integer)
N15:177 50 Block 82 Command 3 Data File Element
This will read the data from N7:50-N7:62 in the SLC-5/03 and place it in the PLC-5 memory at N16:220-232. You can then copy it to the desired location for RSView's use.