PLC 5/250 MSG Instruction
sparky64
May 2003
Newcastle upon Tyne
127
I'm using MSG Instructions to read / write 30 words of data between a PLC5/250 and an SLC5/04.
My MSG Instruction is scanned on condition of an OSR Instruction.
Can someone tell me, if the "MSG Instruction" is capable of transfering the required 30 words of data in 1 program scan.
Cheers
Sparky :)
when the rung goes true the message will then be pending the message is not sent till the end of the scan.
If you look in SLC instruction set help in the help menu of RSlogix 500 it give you a break down of the MSG instruction including max numbers of files that can be sent it varies for diffrent file types but 30 should be ok as long as there not Strings..
Jezz
Depends
The message instruction in the ladder code merely initiates action in the Resource Manager module, which handles the communication and data transfer. Once initiated, the Resource Manager performs the transfer asynchronously to the program scan running on the Processor module.
So completion relative to program scan depends on the amount of data transferred and the length of your program scan, posssibly with some minor influence from whether the data is in the Resource Manager data table or the Processor's.
Hi, I am currently challenging in a new requirement on my new project. We have delivered a project long year ago using DL-250-1 PLC+ 8 point...
1,527
I've got a print-out of old code (PLC-5/250) that I am trying to decipher. I am hung up on an expression in one of the compute blocks. The block...
3,392
Dear Experts, Attached is the photo of old MODICON A250 PLC of CPU type AEG ALU 151-1. PLC & HMI backups are available on below link...
2,950
I was wondering if there is a way to set a new path to the PLC manually in the PV+? They had me change the IP of the PLC's and of course the HMI...
2,358
I have a problem with PLC 5/250 PI. Two (dual reduandant) data concentrators have recently been "locking up" and showing red light on the...
2,135