PLC 5/40 BTR and BTW instruction help
de_arnab
Jul 2006
Louisiana
24
Hello,
I'm new here and looking for some help from you all. I'm writing BTR and BTW instructions in RSLogix 500 for a 1794-IE8 card with 1794-ASB adapter (remote IO) and have some questions on each of these intructions.
On the BTR instruction my length is 9 as it got 8 AI channels and the 9th word is the status word. Do I make it continuous or not ? For the control block, I guess I don't have to set up any values for the 5 words that it uses.
On the BTW instruction, do I put the value -256(decimal for 4-20mA) on the write word 0 of the data file? And, how do I choose the length for this instruction? It's a 8-AI card and the user manual don't say how to choose the length specifically. Also, whether it will be continuous or not ?
I read a lot of knowledgebase tech notes from ab.com but they didn't clarify this with a 5/40 controller using 1794-ASB modules. Maybe I missed it. Any kind of help will be appreciated as I'm doing it for the very first time.
Thanks in advance to all of you.
Arnab
Here's a code snippet from a 1771-IFE, should be similar, notice that the write is only preformed when needed. There is also a good read status bit.
I set up an analog card (1771-IFE/A) in differential mode, this gave me 8 functional analog inputs. I used the RSLogix generated rungs with a BTW...
3,755
I have an application that is duplicated on a similar production line. A 1794-IE8 Flex I/O module is installed and connected to 4 pressure...
2,448
The present system:- Consists of a PLC-5/40 E CPU mounted in a 8-slot chassis. There are several remote I/O panels consisting of five 16 slot...
43
30,124
Hello, I am trying to create a network status map at a plant. I'm assuming the comm status bit of dnet nodes is in the BTR/BTW instruction that...
980
Hello all, I am adding a 1771 VHSC card to an existing system in order to more precisely control part positioning. The problem I am having right...
2,802