PLC 5/40 Download Error
Edwinsky
Apr 2005
Pasig CIty
34
I'm trying to download program from PLC 5/40 processor but this error preventing me from completing the download.
This PLC5 is linked to SLC 5/04 and exchanging datas thru DH+. Channel 0 of PLC5 is connected to HMI and i dont have PCMK card so I use channel 0 of SLC 5/04 OS401 configured to DFI-DH+ pass thru. This error appears on almost at the end of download. RSLinx can see both PLC with no error. I try to switch both plc to program before downloading but I still get this error.
I am using RSLogix5 ver5.00.01 and RSLinx lite ver 2.20.01 on Win98. I am connected to Channel 0 of SLC 5/04 using 1784-CP3 cable
Can you please help me figure out this problem?
Thank in advance
Edwin
You can't post a photo directly from your computer.
Go to photobucket.com & you can upload then point to the photo.
I'd try disabling the messaging between the PLC-5 and the SLC-5/04, then attempt the passthrough upload.
By the way:
Upload: Transfer program from PLC -> PC
Download: Transfer program from PC -> PLC
Thanks Ken. How do i disable messaging? When I switched to program mode both PLC, will this disable messaging?
Sorry, I mean uploading.
Yes, the easy way to disable messaging is to put the controllers into Program mode.
Check the physical connection on the DH+ as well. There should be terminating resistors at each far end of the daisy-chain network (total of 2). If running at 57.6 kb/s, use 150 ohm resistors and if running at 230.4 kb/s use 82 ohm resistors.
I put 150ohms resistor at each end and tried to upload, I got the same error. I disconnect the HMI at Ch 0 of PLC 5/40 and lucky to get connected. I was able to upload the program completely. When get back to DFI-DH+ pass thru connection I was able to get online without any error.
I now scanning the program trying locate what causes that upload error.
Thanks for your replies.
Regards,
Edwin
Good evening, during the download program on a IC200CPUE05 VERSAMAX, after returning the necessary information in the set tempory IP address,the...
3,194
I have SLC 501 processors in my system. After making offline changes to the current program and verifying the project I get an error message when...
4,513
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
115
Hello, I have a machine with a 1756-L72 Controllogix PLC and 1756-EN2T network card, and PanelView Plus 7 HMI. I am using RSLogix V20.05.00...
911
Hi Everyone, I'm unable to download the project to the PLC. I have put the servos to the project and tried to download. Both verifying...
2,258