PLC address error (S7-1200 - TP700 Comfort)

NoName

Member
Join Date
Sep 2003
Location
Domžale
Posts
273
Hello all.

I'm working with a S7-1200 CPU, a TP700 comfort panel and 4 drives that are all connected through profinet.
I've started my project yesterday and have already made a few functions that are displayed on the panel. I'm using about 25 tags so far. But all of a sudden yesterday the panel started showing error messages for some tags.

TagName: PLC address error
Every time I add something in the Step7 logic a new tag gets this error message.
Has any one experienced a similar problem ? I'm going nuts because I can't work on, I'm stuck at this point now.

So far I have tried making a completely new project but it's the same problem.

Any help would be greatly appreciated.

Thanks in advanced.
Best regards.
 
You said "some tags"- so others work fine?
If so- then you might need to download datablocks etc.. to plc

If nothing works, then check HMI connection under "connections"
also go to "online access"
Is HMI and PLC IP there?
 
You said "some tags"- so others work fine?
If so- then you might need to download datablocks etc.. to plc

If nothing works, then check HMI connection under "connections"
also go to "online access"
Is HMI and PLC IP there?

I have rebuilt and downloaded countless times to the PLC, because I also thought that it has to be something that changed there and so the OP doesn't connect to the tag. It's strange that it also doesn't find some some peripheral inputs that can't change.
So far I've solved this by changing the tag properties. I've switched from the symbolic access to direct access. But this can't be the solution to change tags over and over again.

Best regards.
 

Similar Topics

i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
175
Edit: title is wrong: 1756. Sorry. Hello. Is there a way or an instruction to retrieve the CPU IP Address from the program (and assign each...
Replies
10
Views
831
Hi everyone, I am working on a project to protect program memory on Omron CP series PLCs. there is several ways to write protection that i've...
Replies
4
Views
637
Having an issue connecting to my Micro820 PLC. I don't have an IP Explorer and I know its MAC Address is 5C:88:16:D8:E6:65. I'm connected to the...
Replies
5
Views
952
looking for the the MAC address for this PLC, I count find it in the front or at any part of the PLC itself. connected to the PLC by USB, showing...
Replies
11
Views
1,779
Back
Top Bottom