PLC input and output protection/overloads
mavrick
Jun 2015
usa
122
I have a question about overload protection for I/O modules 120v and 24v. I was curious to see is there any reason to protect a input considering it typically has no load on it. Would you protect a 4-20 ma circuit? What brought this up is I was wanting to protect a set of rNO relay contacts going to a 1756-IA161 input card. I couldn't find much on max current for the I/O but it look liked it was rated for 15ma max current with a load. Which is .015 amps. Is there any material to give me a base idea on protecting I/O modules? Thanks
I always add a fuse on digital IO, but nothing on analog for my panels. Some modules have integrated protection, so it may not be needed.
Assuming 15 ma per input, then a 16 input card would draw approx. 1/4 amp total. A fuse such as 1 amp should work fine. The protection for inputs is more to protect the field wiring and devices than the inputs themselves. For easier troubleshooting, I use 1 fuse for each input card.
Output overcurrent protection will vary depending on output types and loads. Some designers put a small fuse in each output for closer protection levels.
+1. I also do the same for each analog for the same reason above. I don't want
any one device to take down the whole system.
I do different things seemingly system to system, but one good option that I have done several times is like jaden fused/breaker the 24V+ seperate for each input/output module.
The downside other than fuse/breaker is that the 24V+ is now different wire number module to module. My main reason for doing this is not to necessarily protect the field wiring or input/output module, but instead to keep power up to most of the system if one section fails. So instead of 1 DI brining down power to all IO, it will hopefully at most only effect 16DI channels, etc.
I normally have one fuse per analog input card, but the plant I'm working in now has a 1/4A fuse on every single analog input. Definitely overkill in my opinion, but it's definitely nice to be able to remove power to a specific instrument without affecting the rest by popping the fuse holder open.
I have worked on systems like that. Very handy with the power isolation per device. It is a bit confusing having the 24V+ be different wired number per device.
Jaden you had mentioned using a 1amp fuse for the input card. IS there a formula or standard used to figure this, example a 20 amp breaker can only be loaded up to 80%. So per NEC it can only be loaded to 16 amps.
Load * 1.25 is usually standard.
Hence, 16 * 1.25 = 20.
If you had a .8A load, * 1.25 would be 1A
Hello everyone. I have a question about Rockwell PLC communication. Now I have a PLC5/30 and a Guardlogix 1756-L71S rack with 1756-DHRIO In my PLC...
1,427
I need one PLC to receive a signal from another PLC. Can I wire the PLC output of one PLC to the input of another PLC? (same voltage of...
3,966
I want to push a button going to one s7-1500 and have it turn on an output and turn on an output on another networked S7-1500. The local part is...
2,131
Hey Guys, I am wondering if it is possible to wire an output from PLC to the start enable terminal (2) on the powerflex 40. as far as i can see...
1,698
Hello everyone I have a Siemens S7-300 CPU 315-2DP, CP343-2P and ASI module .AC2459 I want to using it for test input output . as show in below...
18
4,306