PLC input protection required
AndaMan
Nov 2003
Can your experts here please recommend the practical circuit to protect plc input for digital (24 volts dc.) signal? The 50 level and status swithes will run outdoor ~1000 feet away which are very prone to electrical noise and lightning.
When you mention lightning you're talking some serious issues there.
My thought would be to use a fiber optic link between the components outside and the controls inside. Perhaps you could use ethernet based I/O to a converter such as this
I've never actually done this, perhaps other have and can comment.
A couple of ways;
Use remote i/o modules and connect to your PLC using screened cable and lightning arrestors.
Run each line in screened cable and fit a lightning suppressor to each line. Pheonix contact Trabtech for instance. However I would not reccommend using 24v dc signals with 1000ft of cable.
The best way would be to use a small PLC nearby to collect the inputs and connect to the main system with a field bus system such as devicenet. If interference is a big problem then perhaps consider fibre-optics.
I have a question about overload protection for I/O modules 120v and 24v. I was curious to see is there any reason to protect a input considering...
3,364
Good evening everyone! This is my first post here, after extensive searching on the net I couldn't find an answer to my question so I thought I...
3,490
Hi all, I’m an electrician with limited knowledge of PLC circuits. Typically I will see simple 2/3/4 wire terminations for transmitters on...
26
1,293
I'd like to talk this through a little: Relays are regularly used for PLC outputs, regardless of a need for signal conversion. But what about...
962
See code at the bottom. Hi all. For the story, this is my first complete project using a Rockwell PLC, I've been mostly working with Unity Pro...
811