PLC not following program set
Ok thank you very much trying to get our electronics guy to come look at it , he just keeps saying it’s from Germany and just seems like doesn’t know what to look for
I appreciate that guidance I wish I knew how to test it myself with multimeter or I would by now
Steve Bailey outlined it pretty well, calling out the exact terminal numbers on the Drive to measure. That's the only place you need to measure as that holds both the PLC signal 0-10V and the Ouput voltage to the DC Drive. Again, if possible, run multiple spindles at the same speed and have your tech measure:
Incoming AC Voltage to each drive (should be 230VAC)
Incoming Analog 0-10VDC signal from PLC. Could be anywhere between 0 and 10V, but should be consistent across drives if running same speed
Outgoing DC Voltage from Drive to Motor. Could be anywhere from likely 0 to 90VDC, but should be the same across drives
Then when you do a speed change, both the Incoming Analog voltage and the DC Voltage out to the motor should change somewhat proportionally to your new speed.
Ok thanks again I appreciate it
Another issue I see this morning the HMI screen shows 2 of my stations on the programs “times set”
The word “INPUT I1”
I never put that suppose to be a set time
If you are measuring the Voltage on the drive to the motors and the voltage from the PLC, your meter should be on DC, not AC. The only AC voltage is the incoming 230VAC power supply to the drives.
Input 1 means it is waiting in the previous step until an external Input occurs, then in both cases, it appears to turn on spindle 1. In one instance it turns it on at 350 RPM, then turns on 2 and 3 with it at 350 RPM. The other instance, it turns on Spindle 1 at 180 RPM then changes it and turns on 2 and 3 to 350 RPM.
That Input could be an operator pushbutton, or some indication that some cycle has completed.
In DC setting only 1 of the drive Roxy is at .10
What terminals are you measuring that voltage on? That's awfully low across the board.
What is the DC voltage to the motor?
Are all the Spindles running the same speed during this test?
As a reminder, the 0-10V signal should be measured across terminals X2.5 and X2.10
Motor Voltage measured across terminals X3.13 and X3.14
See attachments
Speed adjusted
Hi all smart and knowledgeable people.I have a hmi connected to 2 Plcs via ethernet.These 2 Plcs connected to control 2 systems in one machine...
76
Hello, We are now working on a software to collet the configuration of different PLC brands ,using a third software to backup all the simens...
61
Dear Experts, I've come across an unusual piece of hardware for AB PLC-5 racks. I mean the NT-1776-HSD-R resolver input module. I have tried...
39
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
196
Hello all. I recently had to re install my AutoCAD Electrical 2024. I am trying to find the Rockwell catalog to install in it but cant find...
96