PLC to PLC Ethernet
Dani610
May 2018
Adelaide
33
Hello Everyone,
I am using two AB ML 1400 that are connected via ethernet switch. Input is given at one plc and output is on the second plc. Now I want that whenever the ethernet cable of first plc is unplugged the output should turn off. what should I do. what is the appropriate approach.
Thank you
Hello Everyone,
Thank you
I am using Rslogix 500 in Vmware workstation 14 player
I am a little confused.
when the Ethernet cable is unplugged, you want the outputs of the first plc to die or the second?
if its the second, I would set up a heartbeat signal between the two plc's.
maybe some can answer as to how, I am not that good at it.
james
james
I want the output on second plc to die
Maybe you could monitor the message error bit if you are doing a read in PLC2 from PLC1.
Alan
Yes i am doing that i have stored the input in an integer bit and then reading that integer bit in PLC2. it reads the data fine but when i unplug the ethernet cable nothng happens
If you are doing a read message in PLC2 of an integer in PLC1 then when the message tries to do a read and the ethernet is disconnected the message should show an error, MG9:0.ER.
MG9 = message file.
Alan
This wont work if you are doing a Write message from PLC1 to PLC2.
below are the codes. i am reading the integer N:20 in PLC2 and storing that in N23:0 then using that to fire output but when i unplug the ethernet cable of PLC1. the PLC2 logic remains the same nothing happens output stays on
MG9 = message file.
Alan
and this is the setup screen of read msg
I cannot read those images they are too blurry, I see you are using a message instruction, instead of a full screenshot just do the message instruction and the message instruction dialog box.
Alan.
thank you all for your feedback i have found a solution now the only problem is that it doesn't start receiving msg when i plug the ethernet cable in again. below is the output logic on plc 2. the enable bit and error bit stays on
If i i don't use the .ER bit in parallel with .EN bit in rung 0 then the .ER bit in rung doesn't work.
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
93
Hi all, My ethernet port on my laptop recently broke and I was hoping to just use a usb-c dongle in the mean time to go live on my PLC until I...
458
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
524
I'm adding an IAI Gateway with 2 axes connected to it. To an ethernet network on my PLC. So, I think the math is correct on the Input and Output...
149
Hello, I've been trying to learn this a while now and still have not found out how this works. I have an Omron CJ2M PLC and an ABB ACS 355 VFD...
255